will a fluorescent bulb work when dc is passed through it??
if not why??
Answers were Sorted based on User's Feedback
Answer / n.jena
Yes,a
fluorescent tube
work on DC
supply,if we
will give a
resistance to
choke in series
connection.for
40watt bulb-166
ohm .
Is This Answer Correct ? | 29 Yes | 0 No |
Answer / debojyoti ghosal
Fluorescent lamps can run directly from a direct current (DC) supply of sufficient voltage to strike an arc. The ballast must be resistive, and would consume about as much power as the lamp. When operated from DC, the starting switch is often arranged to reverse the polarity of the supply to the lamp each time it is started; otherwise, the mercury accumulates at one end of the tube.
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / dwivedi sandeepdhar
no because inductive reactance is zero
Is This Answer Correct ? | 3 Yes | 13 No |
no.because the density of the filament of the fluorescent
lamp is very high for the DC supply.hence DC voltage will
not glow the lamp
Is This Answer Correct ? | 1 Yes | 15 No |
How can decide the MVA rating of power transformer for substation like 220/132, 132/66, 66/33kv etc or even higher kv rating of substation???? Send me the strictly technical answer that shows your strong technical aptitude.
Difference between auxliary relay & pla relay
Is an SCR semi controlled device?
Whether earthmat designning is done only for sub station or it can be done for multy residential complexes also? What is the size, type & arrangement of the earth grid to be done?
A genarator is connected through a 20MVA ,13.8/138 KV stepdown transformer to a transmission line. at the reciving end of the line a load is supplied through a step down transformer of 10MVA,138/69 KV rating .A 0.72 PU load evaluated on load side transformer ratings as base values ,is supplied from the above system for system base values of 10 MVA and 69 KV in load circuit the value of the load in generator circuit will be ...........
Why, the starting current of 3 phase Induction Motor is 7 to 8 times its rated current?
Why transformer rating in KVA? and Generator also?
6 Answers Bhel, IEEE, Toyo Denki, Toyo Engineering,
From an electrical motor & electrical generator, which has more efficiency & why?
All we know about T/R, Is it possible to make T/R primery singlr phase and secondery three phase,If it then how?... Need Description
is it possible to use a tranformer to regulate an unstable system voltage?
dear all, can any body explain that how to select an induction motor for a specific mechanical load(inertia). is there any formula or calculation then please give me. i shell be very thankful to all of you. Thank,s and Rgard,s.
Ammeter of 1 ohm resistance measure max 10 ohm to measure higher resistance from it