WHY THE TRANSFORMER VALUE MEASURES IN KVA INSTEAD OF KW.
Answers were Sorted based on User's Feedback
Meenakshi my view is also very much in line with you said
but addition to above i like to add that the transformet or
a generator are a source and are designed for the load
according to the characteristic & they have nothing to do
with the power factor . As the power factor is not counted
they rated in KVA ( Because KW = KVA x PF vise versa KVA =
KW/PF ) Please correct if something more can be added.....
Is This Answer Correct ? | 10 Yes | 3 No |
any device that acts as a source vil be rated in kva,n
hence transformer,generator,ups etc are rated in kva. n its
not becoz of copper loss n iron loss stories as mentioned
in some books.coz when i answered like this, i was told
wrong.if any improved answer, plz notify me.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / jk
POWER GENERATOR AND POWER USER RATING IN KW
AND POWER TRANSMITTAL DEVICE IN KVA BCOZ THERE IS NO ROLL
OF PF
Is This Answer Correct ? | 0 Yes | 2 No |
how to avoid electrical shock how capacitor store charges wat are the speed control of induction motors state faradays law flemings left hand rule what is rotary converter wat is transmission and distribution what are the sources of energy abrevation of acb,vcb,sf6,igbt what is output equation of transformer which test copper iron and iron loss are calculated what is eddy current draw a single line diagram (10 marks) draw direct online starter(10 marks)
which INDIAN STANDERD in Mention the earth test value?
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
in HVDC transmission system ,monopolar link has one conductor usually a negative polarity and use ground or sea return ?through negative polarity we could pass electricity or not yes means how it is possible
Please mention available current rating for MCB,RCCB,MCCB in the market or any website
What is the difference between vector surge relay (78) and Pole slip relay (98G)
does a DG set has low fault level as compared to that of a transformer.If yes then why.
what is earthing transformer? draw the winding dia.of earthing transformer.
what meant by Locked Rotor Current ?
Can I use 1 phase power supply to run 3 phase motor? If yes, how?
We have laid the single core Armoured cable 7 nos ( 2 each phase & 1 neutral ) to cater our electrical load . the issue is though we have Glanded the cable both the end also givan the earthing to the panel both the end we are facing a heavy sparking at the gland side. what could be the reason.
How to calculate load taken by a cable?