WHY THE TRANSFORMER VALUE MEASURES IN KVA INSTEAD OF KW.
Answers were Sorted based on User's Feedback
Meenakshi my view is also very much in line with you said
but addition to above i like to add that the transformet or
a generator are a source and are designed for the load
according to the characteristic & they have nothing to do
with the power factor . As the power factor is not counted
they rated in KVA ( Because KW = KVA x PF vise versa KVA =
KW/PF ) Please correct if something more can be added.....
| Is This Answer Correct ? | 10 Yes | 3 No |
any device that acts as a source vil be rated in kva,n
hence transformer,generator,ups etc are rated in kva. n its
not becoz of copper loss n iron loss stories as mentioned
in some books.coz when i answered like this, i was told
wrong.if any improved answer, plz notify me.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / jk
POWER GENERATOR AND POWER USER RATING IN KW
AND POWER TRANSMITTAL DEVICE IN KVA BCOZ THERE IS NO ROLL
OF PF
| Is This Answer Correct ? | 0 Yes | 2 No |
How to calculate approximate load loss of a distribution transformer by knowing %ge imp of transformer?
can i connect REF and Differencial relay in 1 CT core for transformer protection?
how much percentage set in transformer diffrencialrelay
What is Star Delta Connection, where it is applied & what for it is used
4 Answers Premium Transmission,
what is the problem of generator over voltage.?except automatic voltage regulator card
How to find the maximum load, that can be supplied by a transformer.....
what are the types of control panel used in industries & all electrical purpose ?
How power factor of a transformer is calculated
Why 36 KV LA is used in 33 KV Line and 9 KV LA is Used in 11 KV Line
1 Answers APTransco, Bhel, Wipro,
you have an automatic voltage regulator at home for your appliances,if the voltage in your area drops from 220v to 190v,does the output of the automatic voltage regulator drops?or does it retains the 220v output?
what is the difference between gas group b and gas group c electrical equipment construction wise?
If I want to replace a 26KW Slip ring Motor with a Squirrel Cage motor & Drive (for a Hoist Application). How can I approximate the Motor & Drive HP required in new Setup.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)