you have an automatic voltage regulator at home for your
appliances,if the voltage in your area drops from 220v to
190v,does the output of the automatic voltage regulator
drops?or does it retains the 220v output?
Answers were Sorted based on User's Feedback
Answer / parveen yadav
it remains same because AVR function is to prevent suddenly
voltage drop and maintain a equilibrium.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / satish kumar dhiman
No the output voltage will not drop but we have to check
the AVR range to control the voltage.
as AVR work on referance voltage produced by another
transformer or device.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / manoj sharma
But my dear friends parveen and shekhar if voltage drops up
to 50V what will happen...if it drops up to 20V hahhaha...i
am serious, at this stage will AVR support? If yes how..If
no why...and what is that limit and limiting factor that
decided the AVR keeping voltage constant ...please clarify
my friens....
| Is This Answer Correct ? | 0 Yes | 0 No |
Define demand factor?
wat is the role of reactive power in power generation?why we have maintain it.
what is the difference between KVAR & KVA ?
11 Answers Bombay Rayon Fashions, Hyundai, Pricol,
some ac motor's direction get change dueto ghanging input to the ac drives.(say ryb to rby). but some motor direction remains the same when phase sequence is changed fromdive side. can anybody guide me?
what is surge impedance loading?
We have 2 Nos. Transformer with the capacity of 2000KVA and 1250 KVA and currently using only one 2000KVA T/R during operational hours while non- operational hous 1250 KVA T/R also used to reduce T & D losses. Similarly, 2 capacitor bank of 500KVAR and 300 KVAR also installed to balance reactive power. Now problem is around 1000 KW load PF is not maintaning 0.99 as 350 KVAR capacitor is in healty condtion. Now the PF is maintain 0.95 to 0.96.
What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer?
how the earhing is done on ship and airplane.
what is differance between PT-100 and thermocouple?
What do you mean by creepage distance?
This is about the recent problem that we have faced in our project site. We have 6/7.5 MVA. 66/11kV three phase star - star power transformer. The neutral was solidly connected to the earthing mat. But because of high resistance of earthing mat (130 ohm on LV and 180 ohm on HV), one day LV side neutral earthing conductor melted and we had a huge damage. Can any one plz tell me what might happen when we connect power transformer neutral to the earthing mat which has high resistance (>100 ohm ) ?????
how to calculate generator capacity?(kva)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)