Answer / ..................
when we say that DG set has 0.8 Power Factor it means
a 1000kVA DG shall deliver 800Watts only.
If we try to load more than this it shall drag more amount
of current. & Ultimately voltage will drop accordingly
resulting in generation of capacitive VARs.
Is This Answer Correct ? | 8 Yes | 5 No |
Most DG's are rated at 0.8 PF. They do not have to operate
at this PF but certain considerations must be taken into
account when the PF is changed.
1 - The kw available is only 80% of the kva rating. This is
limited by the output of the engine. If the load is at
unity PF the output is only 80% of the kva rating.
Otherwise the engine is overloaded.
2 - The maximum current the alternator windings are
designed to carry is the current at the kva rating. If the
PF is below 0.8 the kw load must be reduced to make up for
the extra kvar load so the kva is not above the rated
maximum.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / premkumar
Normal to Design DG p.f is 0.8, some person say Dg set to use APFC with Dual sense Relay for EB and DG side to improve the DG efficiency. Its wright or Wrong.
Is This Answer Correct ? | 2 Yes | 5 No |
Answer / thowsif_emerson
Fristly the design Power factor of the DG set is 0.8, i.e.
capacity of the DG can be used 80%, If you run the DG set
on higher power factor then DG set run on more excitation
due the more excitation the DG set goes to the Capacitive
load when the DG set run capcitve load then current lead to
the voltage. This is the losses of power.
Is This Answer Correct ? | 13 Yes | 17 No |
Answer / sree
Generally at what power factor, DG sets in generating
stations operate ? presuming that the generators run at
0.8 PF, I think it is a loss. what do say?
Is This Answer Correct ? | 4 Yes | 13 No |
why we can not use dc in our country( INDIA)
What is the purpose of Rotor earth fault relay and How to test the Rotor earth fault relay in generators and What is the procedure?.
What is the exact minimum vale of voltage between an earth and netural which can damage or can do malfunction of the electronic equipments ? If this is mentioned in any book, pl.give reference.
0 Answers Bhushan Power Steel,
why is corona loss greater in a stranded conductor as compared to a solid conductor ?
What is reason of rating of transmission line multi pal of 11 like as 11/33/66/220 ? Why not use 75 kv 23 kv line in power system ?
1 Answers Apollo, Balco, Bhel, Vardhman,
What is the capacitance values of 132,220,400 & 765 kV current transformer
What is the restart inhabit setting in ABB spam150c relay (Motor protection relay)
IN MY INDUSTRIES 125 HP MOTOR USED FOR THAT ONLOAD AMPS UP TO 280 SO CAN I USE ONE LOWER KVA DG SET WITH STEP UP TRANSFORMERS THAT MEANS WITH LOW POWER INPUT TO GET CONSTANT HIGH POWER OUTPUT EG:125KVA DG SET = 250 KVA STEP UP TRANSFORMERS
What are different types of control systems?
why rating of motor in HP
what is a pulse transformer? how rise time of pulse changes when ever the voltage changes?
A 150KW 440V motor is need to replace in the field instead of faulty one. what are the main parameter should I need to check?