in 33KV or 66KV system which connection is aviable on high
voltage transformer primary delta or star ?
Answers were Sorted based on User's Feedback
Answer / amit
the question is incomplete it should mention weather it is
load end or at generating end.
at generation end primary will be delta and to nullify
generator harmonic and secondary should be star for
transmisssion line protection as it requires distance
protection.
In load end primary is star and secondary may vary
depending on load condition as load may be 3phase balance
or 3 phase unbalanced load,wether neutral is required or
not.
Is This Answer Correct ? | 6 Yes | 2 No |
In a three-phase full converter, output voltage pulsates at frequency of a. f b. 2f c. 3f d. 6f
the inertia constants of two machines are respectively 30and 42 MJ per MVA.when the change in frequency due to change in load in first machine is 12 Hz,the change in second machine frequency will be?
what is the value of voltage & current lightning during rainy season.
when an induction motor runs on load.at that time if we reduce the supply voltage the current increases.But when it runs without load,if we reduce the supply voltage the current also reduced.why?.i checked it practically also.
What is GNR ? How much value of ground neutral resistance?
how to give earthing in ships?
where is the primary of CT??
A 60W,250V bulb when connected to a 230V supply will it give more light or less or will be give normal light?
CAn a TJM 10 relay measure over current ?
Can any one know what are the symbols at the down (below) the analog ammeter??? there are 4 symbols which are they ?????
As we use capacitor bank in 3ph ckt to improve PF, can we use capacitor in single ph domestric use, in house we have Fan,Mixer,electric cooker,iron,tube choke they also lag the system,because it is inductive load. if it is possible to improve PF of single ph system-- if yes- type of capacitor to be used,connection diagram, working in detail. if no-- list it.
The neutral&earth voltage is 0v.But we were connected the lighting load at the time ballast was failed.why?