Answer / arun.giit
as all the losses is in the form of power;and in transformer
iron loss is directly propertional to voltage(V) &copper
loss is propertional to current(I).it is not depend upon
powerfactor,so it's rating is in KVA.
| Is This Answer Correct ? | 20 Yes | 1 No |
Cu loss of transformer depends upon current I and iron loos
depends upon voltage V...So as we can say that the total
losses of the transformer depend upon VA (volt-ampere) and
independent of phase angle between V & I (i.e. pf
angle)...so transformer rating is in kVA & nt in KW...
| Is This Answer Correct ? | 14 Yes | 0 No |
Answer / tin`
Becuase kVA is the 'total' apparent power. The load
connected to the transformer can have different power factor
(pf) and so the kW rating will vary according; kW=kVA*pf.
The transformer rating is stated in kVA in order to show
the full capacity of the transformer and then the real
power (kW) rating can vary with power factor.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / salim
bcz
kw=kva×pf and load on tranz.is not constant.So pf is varies with load.thats why traz.rating is always in kva not in kw
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mohan singh
Transformer ratings are in KVA because the power factor is
for the load on which transformer will operate is not known
in manufacturing and KW = V x I x Cos Phi.so it is Rated in
KVA and not in KW.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / peter
coz KW or HP makes no sense.....transformer is not a power
conerter involving mechanical energy.....i mean...it just
transfers electrical energy ....
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / bob
Because transformer is power source and active power and
reactive power drawn from it depend on load nutural.
| Is This Answer Correct ? | 1 Yes | 5 No |
what is the meaning of 0.5ohm Resistance
What is the function of pulse transformer?
Distribution Transformer are connected in configuration? a. Star/delta b. delta/star c. star/star d. delta/delta
in cable joints procedure what electrical problems have been solved out ?
i have 60Hz motor, can i run it at 50Hz power supply ???
how we can use resistance heating for any domestic purpose???
What is the slip speed?
what is the diffrence between mcb &elcb?
What is reverse power relay?
how to identify the cable quality and what is flame proof cable
Can we use Motor protection CB while we use the VFD for Speed control?? if not means please tell the reason!!!
why single CT used in DOL starter power circuit?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)