what is the diffrence between mcb &elcb?
Answers were Sorted based on User's Feedback
Answer / pillay
MCB is magnetic or thermal protected over current protection
device. that means if the current flowing through this mcb
exceeds the rating of the mcb it would trip. how fast it
trips depends on how much more than the rated current is
flowing through
ELCB is a device to detect any earth leakage current only.
If the leakage current exceeds the rated current the elcb
would trip off the circuit . The ELCB does not give
protection against overcurrent.
| Is This Answer Correct ? | 12 Yes | 0 No |
MCB - Miniature circuit breaker:- Which helps to avoid over current or fault current enter into the circuit.It protect the circuits by tripping operation.This is available up to 63A.
ELCB - Earth leakage circuit breaker:- Which helps to avoid the running current enter into the earth by means of tripping operation.This is available up to 63A.
ersaravananp@gmail.com
| Is This Answer Correct ? | 9 Yes | 1 No |
WHAT HAPPENING TO TRANSFORMER???? i have the step down transformer rating 230/12v, power rating something.,,, ok. suppose iam giving 12v to secondary side,what will happen on primary side.,,,
what is the clearances between phease to phease & phease to earth in 400 kv transmission line?
how you connect the induction motor first in star and then delta in star-delta starter
can we apply kirchhoff's laws to circuits containing non linear elements?
What is the deffrence between Siemens S7-300 & S7-400 PLC?
explain about RTCC
difference between silent and non silent pole rotor?
What are reasond for high wattage in single phase induction motors
what is the main difference between power devices and signal devices
In Plug used in house,Why Earth of the plug more thicker & deeper?
i want to ask that as everybody knows that in star connection on star point is called neutral. my question is that why on that poin called neutral. what is the reason behind it. what is the logic behind it. i heared somewhere that on this point all phases current become zero thats why. if this answer is right then prove why on that point is current become zero. if this answer is not right then tell me the right answer. post ur answer here or on my mail address. m.ikram786@yahoo.com m.ikram555@gmail.com. thanks.
In our plant we have installed new MCC with ELR and CBCT which is detecting some leakage current in the system but it leading to some confusion when to check that in which feeder which is drawing current we put off the whole panel itself but still CBCT detecting some leakage current so can anybody ans me , where i am going wrong or how to detect whether its actual leakage or CBCT malfunctioning.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)