We in my plant one of the transformer showing neutral to
earth voltage is 22V how to solve it
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Disconnect earth and measure voltages between phases and
neutral on some load.If the voltages are not equal there is
a loose connection in the star point.Before doing
this ,check the earth connection at neutral bushing.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / wasim
Check resistance of earth pit/mesh connected with Start
point (Neutral of Transformer). If reisitance is more than
5 Ohms your Neutral to earth voltage will be increased
accordingly. So you have to improve the resitance of your
earthing network to less than 1 Ohm
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / aditya199307@gmail.com
Such types of problem occur due to increased in value of earth pit.
So 1st you checked the all earth pit values individually by opening all the grounded connections.
As per standard the values of earthing in HT yard should be less than 5volt.
If the value is greater than 5 volt then apply the procedure to reduce the value, which is different as per type of earthing (Normal or Chemical).
If the values should be comes as per rated value your problem is short outed.
If you talking theoretical part then voltage between N & E is zero.
But practically 2 volt is permissible but i.e. also not good for the system
It will affected on electronics system.
Such types of problem occur in the hilly areas or in rocky soil.
( If the value will not coming as per standard then add n....number of earth pits in series otherwise use counterpoise method.)
Is This Answer Correct ? | 0 Yes | 0 No |
What is shutdown of electrical sub station?
what is standard height of an energy meter from ground?
define hysteresis loss, eddy current loss and windage loss
Which phase is prefered for connecting 1phase vt used for synchronism in an OHL? why?
What should be the value of earth resistance for an instrumentation/electronic circuit? As per which IS/IEC Code?
What is the causes Power Factor become leading and what is the effect of Electrical system ?
my UPS suddenly goes off and all panel light also blow off.This happens even main electric supply is not interrupted.After some time it automatically starts functioning normally.Batteries are new.
For a three phase induction motor, what will be the effect on motor if the neutral of the system is shifted to say 20 deg.?
I want to make street light with solar system ... What may I do for procedure and how much of estimation for each material ... If any one knows guide me and inform this id : aravindd7@gmail.com
why the frequency and voltage in india is 230v and 50HZ. when compared to USA say 110v and 60 HZ.
IN OLTC we observed "OUT OF STEP" Alarm, we have two different transformer, when both are in parallel this type of alarm observed. what's the meaning of this alarm and why it occurs???
how can we change the supply frequency?