On LPG sphere tank we used LIT for level indication.High
side port is connected to the bottom of the tank while low
side port connected to the top. I would like to know how to
fill the glycerin on its low side with two condensing pot
installed,one from top and the other one for its drain
line.Please I need your expertise...thanks
Hi there,
This is called a normal wet leg installation. There is no
need to change the HP and LP around when you use a SMART TX.
All SMART Tx can measure in the negative with the same
amount as in the positive. exp: -1600 to +1600mmH2O
Open your manifold vents to atmosphere and do a zero trim,
next close the equalizing valve on the manifold and open HP
line to atmosphere. Fill the LP line until both catch pots
are full and the Glycerin is running out of the top catch
pot into the line going to the top tapping point of the
vessel. At this point let the liquid in the vessel fill the
HP line. Remember to do some draining to make sure there are
no air bubbles. What you need is to have the LP completely
filled with Glycerin and the HP line filled with Vessel
liquid up to the point where the tubing connects to the
vessel(not more). Whatever the transmitter reads now(neg
value)is called an atmospheric zero value(ATM).DO NOT DO A
ZERO TRIM!!
Use this formula to calculate the LRV and the URV
LRV = ATM value + (distance from bottom tapping on the
vessel to 0% point on vessel x the sg of the vessel liquid)
URV = ATM value + (distance from bottom tapping on the
vessel to 100% point on vessel x the sg of the vessel liquid)
LRV and URV UOM must first be in mmH2O if you took these Z/S
measurements in mm. After you install them with the HART you
can change it to whatever UOM you require.
Is This Answer Correct ? | 4 Yes | 0 No |
hi! i want to know about mpse exam.
what is the advantage of submersible level transmitter compare to ultrasonic level transmitter?
while i check zero check for dp flow transmitter some fluctuating came (0 to 458 kg/h) what is the reason?
if we open the inlet of an air regulator ,how it will affect the out put of regulator? (out put of regulator is using to operate an on-off valve.it is an air to open valve,and valve is in open position.my doubt is air regulator will hold the valve in open or not,if there is no consumption or leak in regulator out put side ,we only loose the input pressure.)
Basic working principle of control valves
Can combine control system for Emergency control system (ESD)and Fire & Gas System ( F & G) is possble to built and offer to client? Can such system is as per Norms in India?
What happen if we install my pressure transmitter below the elevation of pipe in natural gas service?
Is there any interfacing sofware to build communication between a PC and ER300P model L&T make trivector meter via RS485 port which is available in the meter and is there any data acquisition card available to store the acquired data from the meter into the system
How is flow measured in square root?
What are primary elements of measuring pressure? Which type of pressure can be measured by these elements?
What is difference of fanuc alpha series 16i and 18i controller.also what is differnce betn TC and MC controller
Dear Sir/Madam,im going to attend Hpcl written exams on feb 17th in instrumentation stream..can anyone send me the HPCL model papers and pattern of HPCL ....i ve not yet attended anything in HPCL...so i dont know how it comes...so just i need some model test papers and pattern ..pls help me friends...