What is shriking and
swell effect for a
boiler ?
Answer / sandip patel
The shrink/swell effect is caused by small pressure changes causing bubbles in the tubes to reduce (shrink) or increase (swell) as a result of small changes in pressure - so that the mixture of steam and water in the tubes remains at the saturation temperature for the pressure at each location
Is This Answer Correct ? | 5 Yes | 3 No |
how to calibrate a capillary type level transmitter for a closed tank in field? also what is the procedure for commissioning a capillary level transmitter for a closed tank?
when an eddy current probe is installed inside of a turbine or compressor in case of probe problem same as:crash of head of probe,changing the scale factor because of low measuring gap(physical gap is ok(example=1.14mm)but voltage is reduced(example=-6 volts),is any way to check the probe,when the ohm of probe is ok.thank you,(Karim Tavakoli)
in valve is constructed as per SME B 16.34, then which standard is used for fire testing of valve?.
Draw a wheatstone bridge circuit showing supply, meter and 3 wire RTD connection
Is there any relation between Artificial Intelligence and Instrumentation?
What is upsampling and downsampling?
what is the importance of CV in the control valves? how it is calculated?
i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500 ltr/hr.) what should i do?
For 150 mtr cable run from DCS panel to transmitter (24 VDC with 4-20 ma output), need cable size. 1.5 sqmm is suitable?
ORP sensor working principle?
how the 2.5bar pressure able to control the 40bar steam
8 Answers IBM, PAFL, Thirumalai Chemicals,
send me last 5 years questions asked in rrb chennai, for section engineer