Answer / s. venkateswararao
check the selector switch auto mode comand, and auto tap
changer time setting lower and upper voltage level setings
to be checked.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / naveen
Oltc worked with reverse- forward motor starter through in built programmed pcb card ,command taken from this card as per voltage observation whether voltage level to be raised or down .Voltage level can be also manually controlled via selector switch.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / guest
I feel its better to call in the experts. Like when I
worked at Reliance, the transformer was supplied by Bharat
Bijlee and their person used to come and do the needful
from Kalwa, Mumbai. Its quite complicated and not easy. So
you are advised to consult your supplier.
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / ams
check AVR setting and check whether AVR is executing the
command correctly.If yes go for further check.
Is This Answer Correct ? | 0 Yes | 2 No |
Once you can try changing phase sequence of tap changing
motor.
Is This Answer Correct ? | 0 Yes | 4 No |
How phase to phase voltage comes 440V.
what is surge voltage and surge current?
How cmd is calculated in case of energy neters
which pump is suitable for home use ?
Why control of DC motor is simpler?
is tree is a good conductor and it may be used for conductor?
how to make a solar panel? why solar panel cell connected to serious?
what meant by Locked Rotor Current ?
1 ph induction motor winding priniple and connection diagram?Similarly for 3 ph induction motor?Full description
In a house wiring why we are using only one neutral wire and so many phase wires from the main board, when the load is common for both wires?
What is the real function of reverse power relay in generator panel while syncronising?
working of diesel generator ?