Why? We r used 50sq. mm. And above size cable in 3.5 core and below size are used in 4core

Answers were Sorted based on User's Feedback



Why? We r used 50sq. mm. And above size cable in 3.5 core and below size are used in 4core..

Answer / k.prakashchandra

Above 50 sq mm cables are usually used 3 phase loads and
fair balancing of loads is expected.As the neutral current
is unlikely to exceed 50 % of full load ,half the core size
is sufficient to save money

Is This Answer Correct ?    2 Yes 0 No

Why? We r used 50sq. mm. And above size cable in 3.5 core and below size are used in 4core..

Answer / diwakar

We even have three phase loads used in 25 and 35 sq.mm.. cant say that as the reason alone.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Can the same motor be operated in both direction ?

12 Answers  


We have drive feeding an output contactor for a 5000 hp motor @ 5kV application. The motor FLA is 629amps x 1.25% service factor = 786.25 amps The cable that we current have in place between the drive and the output contactor is 350kcmil- MV-105 (parallel cables). Per the NEC table 310.60 (C) (69). This show the cable ampacity is at 615 amps per cable for a rating of 1230 amps. We have derated the cable for the cable tray and the multiple cables application and our calculations show that after the correction factor factor we are at 922amps. 1230 amps x .75% correction factor factor = 922.5 amps. The customer is driving us to then use another safety factor of .25% off of the already derated cable. Can you please provide a longhand calculation for your solution on this application?

0 Answers   Siemens,


Hi, My question is our total motor load is 55 kw.so what cable size required for main supply. Please reply

1 Answers   Maryam Enterprises,


in flemings lefthand rule thumb indicate for....

2 Answers   APPSC,


what is the function of bearing in dc mchine" and where it is placed

0 Answers  






What is the voltage gain or transfer function of amplifier?

0 Answers  


Dsitrubution transformer minimum IR value

1 Answers  


What is Instantaneous Earth fault relay,how will work

0 Answers  


Compare OH Transmission & UG Transmission?

2 Answers  


what is the relation between knowing of the distance between power transformer and the capacitor feeder in case of parallel operation

0 Answers  


In a three-phase full converter, output voltage pulsates at frequency of a. f b. 2f c. 3f d. 6f

2 Answers  


I have 3KVA Libert GTX2 UPS. I need to calculate the back up time with some load. How to calculate the Back time. I need the expert guide

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)