in transmiters(rose mount) how to check output 4-20ma ? and
input 24v? i need exact explanation?

Answers were Sorted based on User's Feedback



in transmiters(rose mount) how to check output 4-20ma ? and input 24v? i need exact explanation?..

Answer / anwar mydeen

In rosemount transmitter, open the back side cover which
contains termination.
To check input Power:
switch on the multimeter and select the DC voltage
measurement and connect the positive(red) lead to positive(+
indication in the transmitter) and negative (Black) lead in
the negative terminal(-). then the reading shows 24V DC.

To Check 4-20ma output:

Switch on the multimeter and change the red lead to MA
section and remove one wire from the transmitter and connect
as series. it will show how much reading.

Is This Answer Correct ?    6 Yes 2 No

in transmiters(rose mount) how to check output 4-20ma ? and input 24v? i need exact explanation?..

Answer / carl_ellis

1) Answer #1 is wrong about testing the power supply voltage

With a 24Vdc power supply, the voltage across the
transmitter terminals will never be 24Vdc because a 2 wire,
loop powered transmitter is a current regulator.

A current regulator operates by changing the voltage in the
circuit to regulate the current. The transmitter consumes
some current to operate (3.5mA) and regulate the loop current.

To repeat, to regulate the current, the voltage MUST change.
A minimum loop current of 4mA MUST drop voltage across the
transmitter terminals, it's basic physics.

If one reads 24Vdc across the transmitter terminals, then
there is no loop current flowing because the loop has an
open circuit!

Typically, the 24Vdc power supply positive connects to the
(+) terminal on the transmitter.

If the transmitter is operating and is wired to a typical
analog input with a 250 ohm input resistance, then the
voltage across the (+) and (-) transmitter terminals will be

23Vdc at 4mA loop current (1 volt dropped across the input
at 4mA)

19V at 20mA loop current (5 volts dropped across the input
at 20mA).

The sum of the voltage drops through the loop must equal the
power supply voltage. 23V + 1V = 24V; 19V + 5V = 24V

If the loop is opened by removing the wire from negative
terminal so that no current flows in the loop, then a
voltage test measuring from positive terminal to the loose
hanging wire (that eventually connects to the negative side
of the power supply) will show 24Vdc because the high
impedance of the voltmeter limits any current to the
pico/micro amp level, practically an open circuit.

So, making a voltage measurement across the transmitters (+)
and (-) terminals will NOT show 24Vdc (the power supply
voltage).

2) To check the milliamp output, it is correct that one can
remove the wire.

But nearly all 1151 and 3051 Rosemount pressure transmitters
have a 'test' terminals whose purpose is to allow a loop
current check without opening the loop.

When a milliameter (+) probe is connected to the (+) test
terminal and the (-) probe is connected to the (-) common
terminal, the milliammeter will indicate the loop current.

Using the test terminals does not break or open the loop
circuit.

A HART communicator will show the loop current, also.

Carl Ellis
Measure First

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

Dear all, I'm manikandan I have done by DIPLOMA EEE from 2011 , I have 5 years of experience from Power plants instrumentation field , which one field is give long life & which one field is best ,I confused a lot And also I'm studying AMIE, can I choose which field from Section B examination?

1 Answers  


how to turbine speed measurement?

0 Answers   Jindal Steel and Power,


what is rtd

4 Answers   Petrofac,


what pressure transmitter?

8 Answers   Bhel,


What is the live zero and dead zero

2 Answers   Samsung,






Different between control valve and mov

2 Answers  


Anybody can tell me  how to convert mmHg2o /psi to scfm  please give me formula of conversion

0 Answers   Samsung,


Can a Differential Pressure Transmitter be used as a normal pressure transmitter??

3 Answers  


the output of the common trasmitter protocol in qatar gas are the following

0 Answers  


What is the difference between fiber optic cable & Ethernet cable

2 Answers   BEMCO, CCC, Pidilite,


I want to apply for the universities in US,but i got the GRE score of (650+300=950)TOEFL 69/120.Is this score sufficient for applying universities please i am married i need to go to US because my husband didn't get H1 yet.please send me suggestion

0 Answers  


What are primary elements of measuring pressure?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)