How to check phase R,Y,B
Answers were Sorted based on User's Feedback
Answer / joshykollam
Method 1 . By Color red, yellow , blue
Method 2 . By a Fluke phase sequence meter
Method 3 . By winding lead notation- u1,v1,w1 and u2,v2,w2-
curresponds to R,Y,B in the case of a transformer or motor
The easy way to use Phase sequence meter
Is This Answer Correct ? | 14 Yes | 7 No |
Answer / b shelar
u can be find out easy to use dark-bright lamp method.
Is This Answer Correct ? | 0 Yes | 0 No |
While connecting the flood light plug on to the 415 V distribution panel,there was spark and the cable got burnt. Three ignitors of the flood light also burnt of. The lamps are of 400 W (total 6 lamps) connected through 1.5 mm2 cable. The plug was immediately removed from the circuit. There was a 30 mA RCD connected and a 250 A MCCB; however both did not trip. What could be the possible reasons for the circuit devices not to trip?Can someone assist please. Additional info if needed can be provided.
what is the difference between servo voltage stabilizer and general voltage stabilizer?
whatis the test procedure for lightning arrester which was installed one year back. i want check it whether it is working or not.
how to determine the inrush current of a transformer
How does a star connection and delta connection work? How does the star connection save starting current and how does it change to delta?
In Single Phase AC Supply,If Voltage between Phase and Neutral is 230V means what will be the Voltage between Phase and Earth?
what type of motor used to move a 1 ton gate? and relate ratings with load.
Application of statically induced emf
what is slip ring induction motor? How it works?
What is the difference between sensitive earth fault and restricted earth fault in power transformers?
in Contactor opearation Why there is a difference in the values of the operate and release voltage in case AC supply
Installation method of self treated earth electrode.