In DC while we mention the voltage we are using -48V but in
case of AC we mention only 230V not -230V, why we using -48V
not 48V
Answers were Sorted based on User's Feedback
in the measurement of voltage in any circuit we measure the
voltage of one conductor with respect to another.
In DC supply we have two conductors namely Positive(+) and
negative(-). if we consider 48V DC across the two
conductors, then if we measure the value on the positive
conductor with respect teo the negative conductor the value
is +48V. if we measure the same value on the negative
conductor with respect to the positive conductor then the
value will be -48V. this 48V is the instantaneous value of
the DC supply.
Where as in AC we have two conductors namely Phase and the
Neutral. always the Phase constitute the current path and
the neutral forms the return path. we say that the AC
voltage is sinusoidal. that is it varies from positive to
negative when seen with respect to the neutral.
its impossible to measure the instantaneous value of the AC
supply bcoz it keeps on continuosly varying. so for the AC
supply we consider the RMS value (Root Mean Square Value)
as the voltage of the supply. so in this case there is
always the same value when measured with respect to any
conductor. so the AC voltage does not have polarity.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / naren
when we are measureing dc voltage in negative circuit we
have -48V DC , but in AC there is no negative supplay and
hance we get 48V AC from Phase to Nutral as well as Nutral
to Phase.
| Is This Answer Correct ? | 2 Yes | 4 No |
What is AMF Panel????
What is the Difference Between resistance and resistivity?
Earth has zero potential then what would be the neutral potential ?
WHY WE NEED NEUTRAL FOR 3PH 400 OR 415 VOLTS POWER SUPPLY (4 WIRE SOURCE).
WHEN TWO ALTERNATORS ARE OPERATING IN PARALLEL, EXPLAIN WHY IT IS OBJECTIONABLE TO OPERATE ONE AT A LEADING POWER FACTOR AND ONE AT THE Lagging power factor?
If DG runing time Neutral earth connection Dissconect what will be the effect in load and equipments.
I have 2500KVA transformer delta/star,13.8KV/380V provided with LV 4000A breaker. Already I have 2300KW motor feeder with a full load 90%. Is it possible to connect another 1600A from that breaker? If so how the calculation is done?
what is the difference between HV and LV Breakers?
4 Answers GM General Motors, OEG,
For household Load of 11Kw supplying 5Nos. 1.5 ton Air conditioners + usual other load what shall be rating of Either ELCB Or ELMCB? Which of the circuit breaker will be a better choice?
explain safety measures in alternator?
What is E.M.F ?
why should a transformer be never connected to dc supply
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)