how the 2.5bar pressure able to control the 40bar steam
Answers were Sorted based on User's Feedback
Answer / mohamed yousuf(instrumentation
according to the formula P=F/A
Actually we are applying the 2.5 bar pressure to the
diaphram actuator. By increasing the area of diaphram we
can increse the force acting on the diaphram and that muuch
of force is more enough to actuate the stem movement.even
though 40 bar pressure is applied only to the small area
(plug of the control valve).the force actiong on it will be
very small.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / waseem ahmad
Mr. Bipinchandra is right but there are more possible
answers to this. 1) what is the differential pressure across
the valve? the pressure of steam might be 40kg but the
pressure of steam across the valve might not 40kg. 2) the
use of balanced plug in control valves allow us to control
high pressure fluids with minimum actuator force.
| Is This Answer Correct ? | 4 Yes | 0 No |
the 2.5 bar is used to control the valve by giving it to
the diaphragm to actuate it.so the process pressure 40bar
is controlled.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / bipinchandra ravalia.
The 2.5 bar used to control the valve acts on the
Diaphragm. Now the area of the diaphragm is Large and thus
the Force Per Unit Area acting on the stem is very much
greater than the Process pressure of 40bar. Thus it is not
difficult to control this process pressure with the given
2.5 bar air supply to the control valve.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / sagar,kptl
By using of pneumatic control valve,that control valve have a helical spring containing tension when give pressure 2.5 bar. That pressure force acting will control the 40 bar steam
.'.P=f/a
| Is This Answer Correct ? | 1 Yes | 0 No |
That's why in high pressures line(like super heater's steam in power plant) having double seated globe valves.therefor double seated plugs has line pressure both side equal (upside same and down side same ) is equal to line pressure 0
So thus, plug will operate according valve's pressure.....
| Is This Answer Correct ? | 0 Yes | 0 No |
find the kp ki kd from the transper function G(S)=29.44s+04707/1.5349s2+s
Q- voltage source of 12v is driving the circuit.if circut draw the current of 0.5A them source voltage will became 11.8v.what is the power dilevered by source when circuit draw 5A current ?
what is plc communication?
How Many Slave Can be used in one slave ?
How to calibrate DP transmitter by using HART communicator ?
how to caluculate flow by using transmitter?tell me plz I am eagerly waiting for your reply..
2 Answers Agi Glaspac, Reliance Power,
Name four general (not technical) criteria that would you consider important, when deciding upon a particular control valve?
What is scale factor of proximitor & unit of the viabration.
why we go for pcbs
Give me a simple formula to calculate the bore of orifice plate with datas avilable instead of BS 1040.I want to calculate the approximate bore size only.
What is the difference between PLC and DCS?
How to change dcs card in online. (Dsc is maxdna)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)