How to calibrate DP transmitter by using HART communicator ?
Answer / sunilkumar tailor
Step:
*Ask panel man to put the controller in manual mode for control loop and to put it on MOS for ESD loop.
*Hook up HART Communicator and verify some parameters by refer to data sheet. Typical parameters are, tag number, PV, LRV and URV.
*Isolate the instrument from the process.
WARNING – If the process is hazardous, please unsure proper flushing is done to remove the entire hazard.
*Open vent valve at drip ring and open plug at the top of the drip ring (if available) to release the process pressure
*Clean the liquid inside the drip ring and put back the plug for high side only (if available).
*Expose the low side to atmosphere
*Hook up a multimeter in series with the signal to the DCS to measure current signal.
*In this condition both capillary flange will be atm pressure at difference high
* Multimeter should show 4mA and PV at HART communicator should shows 0 (LRV)
*If not, do zero adjustment at transmitter using HART Communicator
*Connect pressure calibrator to high side flange (drip ring)
*Apply pressure depend data sheet span (URV)
*Multimeter should show 20mA and PV at HART communicator should shows same with URV
*If not, do span adjustment at transmitter using HART Communicator
*Verify the linearity by increasing and decreasing the pressure (0%,25%,50%,75%,100%,75%,50%,25% and 0%of range)
*After completion of the job ask panel operator to put loops back in normal mode or normalize the MOS
*Fill the calibration form and file it for future reference.
Note:
Capillary flange at same elevation
Example calculation:
Transmitter range = 0-2 kg/cm2
LRV = 0 kg/cm2
URV = 2 kg/cm2.
Is This Answer Correct ? | 5 Yes | 0 No |
there are two candidates p and q in an election.During the campaign,40% of the voters promised to vote for P ,and rest for Q.however, on the day of election 15% of the voter went back on their promise to vote for P and instead voted for Q. 25% of the voters went back on their promise to vote for Q and instead voted for P.suppose,P lost by two votes,then what was the total no. of voters.
what is function of DCS , and how is it work , explain with difination
1 Answers Bapco Bahrain Petroleum Company,
Why Instrumentation Air Compressor called as Instrumentation Air compressor?pls dont just tell its trasferring IA to all transmitter,valves.I need exact reason, please......................
Reasons for using seal pots:
if my flow is 20000 m3/h than which range of DPT i have to use????
what is the deluge ? How can its working?
What is the input impedence of an OPAMP as an ideal device.
please tell me five types of fault of control valve and positioners?please
Explain why use mmwc unit?
If we increase PI controller what will be action.
Hi, I'd like to know the purpose of MOS (maintenance override switch). At site, these switches are installed in a stanchion with the transmitter (connected to ESD). thank you.
3 Answers Adani, Adani Wilmar,
What is the Difference between E/P Positioner and I/P positioner in a control valve? In which applications the respective positioners are used in?