i have D.p. transmitter of range 0 to 2540 mmWC, i want to
use this for flow measurement (0 to 500 ltr/hr.) what
should i do?
Answers were Sorted based on User's Feedback
Answer / g.ramakrishnan
to install flow transmitter and correct range
orifice,ensure that ft output is linear means dcs side u
have to make sq root.if smart type transmitter means
configured sq root output field itself.then u will get
correct reading.
Is This Answer Correct ? | 17 Yes | 3 No |
Answer / bari
Install appropriate dp flow element in the flow line with
Beta ratio corresponding to dp of 2540 mmWC for flow of 500
ltr/hr.
Is This Answer Correct ? | 14 Yes | 5 No |
Answer / raees mansoori
use this formula to dcs side Q=K*A*sqrt(H/P) or configured
sqrt output to transmitter side.
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / k.sreenivasan
Mr.PasavaRaj,
Your question misses a major point.
Do you have a flow sensor (like orifice or annubar etc)
already installed?If yes, Then you have to match the DP
required by the sensor to the transmitter DP Range.Please
note that 2540 mm wc of the transmitter range can be
changed using communicator (If it is HART) based on
transmitter specifcations.Check what is the minimum span
the tranmitter can be calibrated? if that is greater than
the sensor DP, you have to look for another transmitter.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / pasuvaraj
mr Raees,
Can u explain wat u mean for H & P in this formula, and
also can u explain how the pressure units convert in to
flow rate in the transmitter. I Mean that mm of water colum
is converted into Mass or volumetric flow can u give me the
answer
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / jigarsinh vaghela
First of all Good Question
Ans: Use Orifice Bore Calculation sheet
you want process data like pipe size, Max Temp, Max Pressure,
Max Flow rate & Application like Steam or water
put this values in OPA Calculation sheet & you would got dp
range in MMWC
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nadeem iqbal
Dear Sir,if i have flow transmitter range 0 to 2500 mmwc and my DCS range is 0 to t m3/hr ,i m getting 9 Ma how much will be the delta P
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sanjay
by creating proper DP across orifice plates we can measure
flow rate also change the SQRT property in x-mitter
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / guruprasad s.v
i am guruprasad honewell employer.
defenetly we can change configure, this fecility is there
in our company.
Is This Answer Correct ? | 5 Yes | 8 No |
How a pH sensor & analyzer work at waste water treatment plant, whats the principle & science is beyond this,How pH sensor sence & convert signal & move toward analyzer & analyzer show reading in percent? also what is temperature compensate option in analyzer
Explain Gas Turbine startup and shutdown sequences
how is a displacer type level transmitter calibrated.explain the method?
what type of cables are used for f&G systems and detectors, what is the standard colour?
What kind of feedback is used in DP cells.
Can be operate control valve without positioning if yes ? how and why?
what is written on orifice plate?
how to work static pressure sensore how to work dpt
WHAT IS D/O D/I AND A/O A/I PLZ EXPLAIN
what is mean by hot loop and cold loop testing, whts different between both
why we are using digital signals for I/O & how to measure this signals is getting or not ?
A pressure differential gauge type of instrument has a manifold with 2 isolation valves (hp and lp),2 vents(1 each for hp and lp) and 1 equalizing valve. Determine the position of each valve(either fully closed or fully open) when troboulshooting to: 1. zero the transmitter. 2. determine if there is a block in the impulse line. 3. determine if the gauge is functioning properly. The process fluid is water.