Sir
Power transformer :- (in generating station)
Alternator terminals side - Delta
HT transmission line side - Star
Why?
Answers were Sorted based on User's Feedback
Answer / anup mohan
I could not understand the question clearly... but.. in generating n transmitting the terminals are in delta... as we need only 3 phases..... but at the other end.. i.e on the distribution end.. the connections are in star/wye... thtas ca.. in addition to the 3 phases we need a neutral... we ve neutral conection only in star and not in delta
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / nagarajan
Example 15mva,220/132kv
Star 220kv here phase voltage =line volatge/1.732=127kv
delta 11kv here phase voltage =line volatge.
Because star side we have neutral ,a.insulation cost less and 127kv insulation is sufficient but in this delta we require 132kv insulation.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kc
To reduce the fault level
The fault on primary side ie Y (LLG)
Will reflect as a LL Fault
So fault current level will b less
No zero sequence current ll b appar on d secondary side
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / bhim kumar yadav(l&t)
bcz in delta side voltage is more compare to star side. so
insulation cost is very-very high in delta side compared to
star side.therefor, we keep always star connection in HT
side
| Is This Answer Correct ? | 2 Yes | 3 No |
What is fault.?
2 Answers AngloGold Ashanti, MNC,
Why lightning arrester blast in rainy day?
1 Answers Eco Cement, Mahaveer, MBDL,
In any plant or substation main incommer voltage RY - 415 V,YB - 400 V, BR - 387 V(in commer feed from transformer 11 Kv /0.415 KV) why found voltage differance in each phase? plant have not self power plant it is depend on outsource grid
What is difference between ON delay and OFF Delay Timer?
What is an ac motor?
Hi How can you start-up the 40w tube lite with 230v AC/DC without using any choke/Coil.
what is the difference between UPS and INVERTER?
Why we use shunt coil in breaker??????????
why the generator operating along with the infinte bus bar should never be under_excited?
What is Hi-Pot Test for Grid Station HV Equipments?
For a three phase induction motor, what will be the effect on motor if the neutral of the system is shifted to say 20 deg.?
how much cable size required for 70 kilowatt load.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)