how to caculate no load loss, load losses & impedance
percentage in power or distribution transformers
Answers were Sorted based on User's Feedback
Answer / den
WE CAN'T CALCULATE THE POWER LOSE BECAUSE THE CKT. IS OPEN
AND THERE IS NO FLOW OF CURRENT.**** thanks
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / den jagus
we can't Calculated the power lose of an open ckt. Because
there is flow current.**** THANKS
Is This Answer Correct ? | 0 Yes | 0 No |
we can calculate no load loss of TR, but you need to know impedance of TR
Is This Answer Correct ? | 0 Yes | 0 No |
Short the LV side ,increase voltage on HV ,till you get the rared current. The percentage of this voltage against rated voltage is % impedance . if you connect a watt meter you get copper losses . With open circuit apply rated voltage ,to measure the iron losses with a watt meter .
Is This Answer Correct ? | 0 Yes | 0 No |
If a line which is drawing approximatly 2100amps what should be earthing streep size(using galwanize streep)?
What is the Good Earth resistance value of G.I & Cu. Chemical Earthing & Normal Pipe Earthing?
0 Answers ABC, Reliance Life Sciences, TCS,
What is different between hypo test and megger test
What is servo motor? what is its purpose?
at work i have a genertor/alternater what is the easyest way to work out if it is dc or ac?
Mention the disadvantages of low power factor? How can it be improved?
What are the effects of electrical faults?
how can you calculate fault level ?
what is the load amp for 1 HP 3 phase Motor ?
how to extend relay operating timing in 24V dc relay card (without using Timer )
110 KW MOTER DOL STATER 240SQ.MM CABLE MOTER AND STARTER DISTANCE IS 110 METER WHAT IS VOTAGE IN MOTER END AND SYSTEM VOTAGE IS 415 V HOW I CAN CALCULTE
describe your self.