Answer / naren

transformer having two kind losses .core losses and copper
losses . former depend on voltage while latter on current
so that why transformer rating is in KVA .

Is This Answer Correct ?    14 Yes 6 No

why the rating of transformer in only KVA not in others?..

Answer / ashwin

prakash i am fully satisfied with your nswer,as we have noidea of load on transformer.

Is This Answer Correct ?    0 Yes 0 No

why the rating of transformer in only KVA not in others?..

Answer / vikram chandorkar

as we know that every electrical machine is having losses..transformer is having two kind of losses i.e core loss which generally depends on voltage and other is copper losses (i.e I2R losses)which depends on current.hence transformer rating is given in kVA

Is This Answer Correct ?    0 Yes 0 No

why the rating of transformer in only KVA not in others?..

Answer / b.anil kumar

transformer is designed to supply full load current,that
means it is independent of load power factor.so it is in KVA

Is This Answer Correct ?    1 Yes 2 No

why the rating of transformer in only KVA not in others?..

Answer / prakash

1.Power factor of the load in not defined in case of
transformer, so it is not possible to rate transformer in KW.
2. The losses (Copper loss and current loss) of the
transformer depends on current and voltage not on load.
3. Transformer is not a load and having no effect on PF and
its only transfer the constant power from one voltage level
to another voltage level without changing frequency.

Is This Answer Correct ?    1 Yes 2 No

why the rating of transformer in only KVA not in others?..

Answer / khalid

because of transformer winding losses
winding loses are a reactive power reactive power is add
in active power so the rating of T.F in KVA
KVA = Apparent power
KVA =KW+KVAR
Apparent power =Active power+reactive Power

Is This Answer Correct ?    0 Yes 1 No

why the rating of transformer in only KVA not in others?..

Answer / elango

the manufacturer does not know what type of load will be
used by user(it may be resistive ,capacitive , or
inductive) so it is all dependent on power factor. so only
it is rated in VA or KVA

Is This Answer Correct ?    5 Yes 7 No

Post New Answer

More Electrical Engineering Interview Questions

what curve and rateing would you use for a three phase 0.75kw motor?

0 Answers  


what is surge voltage and surge current?

2 Answers   MES,


why we are using earth pit in sub stations.?

0 Answers  


why the pressure coil is not present in the three phase wattmeter?

1 Answers  


WITCH CARDS IN USE IN FIRE CONTROL PANEL.

0 Answers  






WHAT HAPPEN WHEN CT SECONDARY OPEN DURING LOAD

16 Answers   Neco,


Can anybody tell the formula to calculate temparature rise in the cable with respect to current?

1 Answers  


On monitor it is written that current rating is 2.2 Amps. Is it a monitor current drawing capacity or CPU & monitor. If it is only monitor rating, what will be the rating of only CPU and what will be the power consumption rating of PC, Monitor & Scanner? In net, I learnt that computer consumes only 200-300W while running. With the current rating of 2.2 Amps, how it could be 200-300Watts. Please explain?

3 Answers  


A double circuit with dog conductor 66KV Transmission line from wind farm evacuation to feeding substation having capacity of 25MW for transmission. Can same transmission network be considered for further expansion of Power & how much in MW. If we need to expand next 10-15 MW more will there any augmentation is required in transmission network? Kindly reply asap.

0 Answers  


sir i used 3 hp of motor for spraying pump, other home light and other home items which size of allminium pvc wire ix used

0 Answers  


what is difference between mccb,mcb,elcb,pccb

7 Answers  


what is meant by dielectirc medium? what is the dielectirc value of air and water???

2 Answers   ISRO,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)