How to calculate cable size for a particular load? i have 12
MW,11KV Motor 3 Phase, what should be cablesize?
What are the points to remember for cable sizing calculations?
Answers were Sorted based on User's Feedback
Answer / mahesh sali
For Cal.the cable size , pl. see the below size
1) Cal. the full loasd current of motor
2) cal. the voltage drop from ht starter panel to motor at
starting and running .
3) as per IEC rule u should take the 20% additional to ur
selected size of cable.
Base on the above step we can easily cal. the size of cable
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / manoj
Calculate steady state voltage drop and motor starting voltagedro they should be within limit also the short circuit withstand capacity to satisfy i2t
Is This Answer Correct ? | 0 Yes | 2 No |
suppose MCC (Motor control center)panel work on field the relay on this damage or not work and earth fault occurs in this and no indication in relay panel given below. than MCB trip or not and what effect the panel how find relay will damage or not work.
11 kv input, 66 kv input advantages
What is the high tension lines voltage and low tension lines voltage?33 kv is high tension line or low tension.
what is the apt definition for kirchoff's current and voltage laws?
whu does the power factor of diesel generator always be 0.8. please explain
why PD testing for power cables
1 Answers Bhushan Power Steel, CSE, Datre Corporation,
How can I known multiplying factor .without multiplying table
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
why we use ac supply as 415 volts instead of 415 v why we cant apply 230 v for dc
explain Xmer
Why we use parllel operation of alternator
how can 3phase motor speed can be controlled without vvf drive?