How to calculate cable size for a particular load? i have 12
MW,11KV Motor 3 Phase, what should be cablesize?
What are the points to remember for cable sizing calculations?

Answers were Sorted based on User's Feedback



How to calculate cable size for a particular load? i have 12 MW,11KV Motor 3 Phase, what should be ..

Answer / mahesh sali

For Cal.the cable size , pl. see the below size

1) Cal. the full loasd current of motor
2) cal. the voltage drop from ht starter panel to motor at
starting and running .
3) as per IEC rule u should take the 20% additional to ur
selected size of cable.

Base on the above step we can easily cal. the size of cable

Is This Answer Correct ?    5 Yes 3 No

How to calculate cable size for a particular load? i have 12 MW,11KV Motor 3 Phase, what should be ..

Answer / manoj

Calculate steady state voltage drop and motor starting voltagedro they should be within limit also the short circuit withstand capacity to satisfy i2t

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

suppose MCC (Motor control center)panel work on field the relay on this damage or not work and earth fault occurs in this and no indication in relay panel given below. than MCB trip or not and what effect the panel how find relay will damage or not work.

2 Answers  


11 kv input, 66 kv input advantages

0 Answers  


What is the high tension lines voltage and low tension lines voltage?33 kv is high tension line or low tension.

1 Answers   MPSEB,


what is the apt definition for kirchoff's current and voltage laws?

3 Answers  


whu does the power factor of diesel generator always be 0.8. please explain

5 Answers   Dalkia,






why PD testing for power cables

1 Answers   Bhushan Power Steel, CSE, Datre Corporation,


How can I known multiplying factor .without multiplying table

0 Answers   Student,


234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,

0 Answers   Jubail O&M,


why we use ac supply as 415 volts instead of 415 v why we cant apply 230 v for dc

0 Answers  


explain Xmer

2 Answers  


Why we use parllel operation of alternator

1 Answers  


how can 3phase motor speed can be controlled without vvf drive?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)