Answer / sandep
load is depend on p.f.
say pf=1 then load is=10kw and 25kw
for pf .9 then load is=9kw and 22.5kw
| Is This Answer Correct ? | 49 Yes | 10 No |
Answer / aruloli
Dear Friend
You forgot to furnish few more data i.e Voltage rating of
primary and secondary.
If i assume Voltage rating for 10 KVA Transformer as 230
V/110 V (Primary/secondary)and considering as single phase .
primary load current is calculated as
P=VI
10*1000(VA)=230*I
I=43.47 A
Secondary current is ,
90.90 A
Considering Transformer as 3 phase, then
P=1.732*v*I
Primary load current is
10000=1.732*230*I
I=25.10 A
Secondary is,
52.48 A
| Is This Answer Correct ? | 35 Yes | 15 No |
Answer / k.sri405
10 kva & 20 kva means transformer apparent power that is
combination of active and reactive power so we can load this
transformer below its rating coz load means only active
power .but in case of purely resistive losd we can load this
transformer upto its rating but practically purely resistive
load is not possible.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / kaleem
aroluli which voltage we'll use ? line to line to line to line to ground ?? 230 or 400 this formula to calculate 3 phase current ?? p= 1.73 v i cos@
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / dkverma67
For 3phase transformer
10 KVA=10*1.4 Amp=10.4 Amps maximum
25 KVA=25*1.4 Amp=35.0 Amp max.
| Is This Answer Correct ? | 8 Yes | 9 No |
Answer / pillay
the max load you already said as 10 kva and 20 kva. In terms
of kw it will be 10 & 2o kw also, so long it does not exceed
10 & 20 kva ampere ratings.
| Is This Answer Correct ? | 5 Yes | 6 No |
I'm looking for a mnaual set for a Teradyne J750. Softcopy would be preferred but I'll take what I can get.
What is the Working principle of ELCB and RCCB?
what does hapen if suddently frequency doubled
Why do you get a typical sound when the transformer is put into operation?
how we do Vector group ,magnetic balance and tap changer test in Transformer?
how can we test the polarity of a 3-phase transformer?
Different STANDARDS (BS, IS, IEC etc) gives different informations on CT specification. How they correspons w r t each other (i.e I mean to say BS provides "knee point voltage" but IS does not, then how can i select CT)
What are the advantages of vscf wind electrical system?
Car battery + terminal allways biger than - terminal! Why?
How is The split core current transformer working ?
Who is the first Bangladeshi Everest climber? Where is his home district?
what are the types of control panel used in industries & all electrical purpose ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)