what is the maximum load on for 10 kva & 25 kva transformer
Answers were Sorted based on User's Feedback
Answer / sandep
load is depend on p.f.
say pf=1 then load is=10kw and 25kw
for pf .9 then load is=9kw and 22.5kw
Is This Answer Correct ? | 49 Yes | 10 No |
Answer / aruloli
Dear Friend
You forgot to furnish few more data i.e Voltage rating of
primary and secondary.
If i assume Voltage rating for 10 KVA Transformer as 230
V/110 V (Primary/secondary)and considering as single phase .
primary load current is calculated as
P=VI
10*1000(VA)=230*I
I=43.47 A
Secondary current is ,
90.90 A
Considering Transformer as 3 phase, then
P=1.732*v*I
Primary load current is
10000=1.732*230*I
I=25.10 A
Secondary is,
52.48 A
Is This Answer Correct ? | 35 Yes | 15 No |
Answer / k.sri405
10 kva & 20 kva means transformer apparent power that is
combination of active and reactive power so we can load this
transformer below its rating coz load means only active
power .but in case of purely resistive losd we can load this
transformer upto its rating but practically purely resistive
load is not possible.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / kaleem
aroluli which voltage we'll use ? line to line to line to line to ground ?? 230 or 400 this formula to calculate 3 phase current ?? p= 1.73 v i cos@
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / dkverma67
For 3phase transformer
10 KVA=10*1.4 Amp=10.4 Amps maximum
25 KVA=25*1.4 Amp=35.0 Amp max.
Is This Answer Correct ? | 8 Yes | 9 No |
Answer / pillay
the max load you already said as 10 kva and 20 kva. In terms
of kw it will be 10 & 2o kw also, so long it does not exceed
10 & 20 kva ampere ratings.
Is This Answer Correct ? | 5 Yes | 6 No |
what is earth pit , how we can measured it, what earth rods reference
How to test transformer
waht is the working principle of saft starter & what is the difference in vfd & saft starter
what is the meaning of electrical maintenance?
3 Answers GE Healthcare, MAHINDRA,
Why short ckt does not happen when solenoid coil connected to supply. as its a wire only.
What are ampers.30kw motor.440volts.
I need a 33/690V Dry type transformer.How to select IP class for this transformer.This will be an outdoor transformer located in a highly polluted environment.
what is the difference between rectifier and converter and commudator?
If i want to build 230kv substation what are the equipments to be installed?
Supose we have one 220v A.C fan.if we provide 220v D.C what will be happen?
what is the difference between AC choke (inductor) and DC choke (inductor), working and design point of view?
I am having a DG set.The 415 V from Generator is step up to 460 v and then the same is used for Induction furnace. before Step up, I am connecting LT load to my factory use. When Induction furnace is in service from DG, when i try to start a motor, the generator is tripped.Please tell me the reason.