WHAT IS B & C CLASS SURGE PROTECTION AND WHAT IS DIFFERENCE
BETWEEN B & c CLASS SP
Answer Posted / dhiraj banka
Class b SPD is for lightning surges & class c SPD is for switching surges.Class B+C protects both from lightning & switching surges.
| Is This Answer Correct ? | 8 Yes | 3 No |
Post New Answer View All Answers
1. If 8.35%Z means the percentage impedance of 132kV-line from power company, we will like to reconfirm its base capacity.
when ac current flows thru d coil of a contactr,it energizes,magnetic field attracts d contact of the coil...nw wont dt ac current in d contct induce current back on to d coil thru mutual inductance leading to high currnt in d coil
What will happend if given Vfd out put to step up transformer
in basic 2 phase will short means tripping the power but spot welding 2 phase shorting but not tripping it will welded why.....(Q)
how we select ac fuse rating of an power inverter???
what is the use of piston rings in the engine used for a generator...........
WHERE NEUTRAL WIRE IS CONNECTED AT DOMESTIC TO TRANSMISSION LINE(SINGLE PHASE TO THREE PHASE)
what is a bus post insulator? explain its application in a substation.
How short circuit MVA(Fault MVA) in a power system calculated for calculating number of earth plates ?
in battery charging room we find two fuses (one in positive other in negative cables ).why it is so?one fuse is ore than sufficient?
how can calculate resistance box for 15 kw, 6 pole, RV-230, RA-42 motor
I am abt to give IOCL intrv.Plz sir guide me for IOCL intrvw (Electrical).Which subject to be consider. questions are generally asked from which subject.Plz help me out.
What is the use of bundle conductors?
3ph motor running with unequal kw and different pf what are the reasons
PLZ EXPLAIN THE INTERLOCKING AND CONTROLLING OF CONTACTORS????HOW CAN I DO THAT?