Answer / gopal
bushing which is used to insulated the terminal to the
transformer body,it is made my porseline.the size of
bushing depand upon the input output voltage
Is This Answer Correct ? | 20 Yes | 1 No |
bushing is an insulator which protects the transformer tank
from being connected with live suppy terminals.generally
made of porcelin,having conductor rod through the channel
inside it and also having a current transformer
arrangement.oil is filled between the connecting rod and
inner cylindrical surface of porcelin cylinder. the
porcelin cylinder has a petty coat shape to protect this
unit in rainy days. In a word, bushing is a protecting
insulator which protect the tf from flashing over.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / raj
Bushings are useing only instator provied between t/r
boby..
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / kabir0921
Bushing is an arrangement in transformer which provides the
path of conductor from high voltage line to transmission line.
It protects the transformer from flash over.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / raj
bushing is the instrument that is an insulator between the
tf tank and primary and secondary windings
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / m.baskaran
bushing is the instrument that is an insulator between the
tf tank and primary and secondary windings
Is This Answer Correct ? 0 Yes 0 No
Is This Answer Correct ? | 0 Yes | 0 No |
what are the types in Relay?
a 440v 60hz 03 phase 100kw generator can deliver how much power in kw for 220v 60hz 01 phase load?
if 2 coil of 1000W connect in series and 200 v is applied across it . then what is the total power of coil when coil have only resistive load .
Why insulation level follows this order? transformer < bus bar < circuit breaker & Isolator < transmission line.
What is the life of MCCB
If ct ratio is 250/1 and mtr is of 5 amp, what will be mf?
What is fault clearing time for Current Limiting Moulded Case Circuit Breaker?.
How you will determine the volume of oil in a particular Distribution transformer.
A motor running with lenze frequiency inverter stops if I REDUCE SPEED with 25% load.If I run it in High speed and medium speed running smoothly with full load.please help me to solve it.
11 kV line deraction check by an Engineer.
I am a possesor of c licence from 1993. I forgot to renew during the year 1998. During that time I was working at TNEB to till date. Is there any possibility to get renewed? or to apply for a new one?
Why alternators are rated in KVA?