what is specific gravity of a battery
if specific gravity increase/decrease,what will happen to
the voltage/current of the battery
Answers were Sorted based on User's Feedback
Answer / subash konar
Density with respect to water.If it decreases efficiency of
battery becomes low thereby decreasing current and voltage.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / harish kuqhsal
SPECIFIC GRAVITY OF A BATTERY IS THE ENERGY DERIVED PER UNIT
WEIGHT OF THE CELL. WITH THIS THE VOLTAGE AND CURRENT IS NOT
AFFECTED.
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / manoranjan
Specific gravity is the ratio of the weight of a solution to
the weight of an equal volume of water at a specified
temperature. Specific gravity is used as an indicator of the
state of charge of a cell or battery. However, specific
gravity measurements cannot determine a battery's capacity.
During discharge, the specific gravity decreases linearly
with the ampere-hours discharged.
so specific gravity depends on volage/current.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / vinod
its change with the cherge or discharge the battery.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / vishal ingle
It is an indication about the charge storing capacity of a
battery. If sp. gr. decreases / increases, it affects the
voltage across terminals merely but the back up provided
will be affected adversely. In simple words, the battery
performs optimally near to the standard sp gr of 1200.
| Is This Answer Correct ? | 0 Yes | 0 No |
In LT cables 3.5 core cable are available that means 3 core and .5 for neutral Why .5 for neutral and is there any reason for that please suggest thanks and regards pavan kumar
We have laid the single core Armoured cable 7 nos ( 2 each phase & 1 neutral ) to cater our electrical load . the issue is though we have Glanded the cable both the end also givan the earthing to the panel both the end we are facing a heavy sparking at the gland side. what could be the reason.
Recently we had experienced following problem All RCCB breakers (connected to the load as well as spares) connected to various UPS systems at various floors at a high rise building tripped during a power break down and upon starting up of generator.This Generator is recently inducted into the installation. Can any one explain the reason behind this tripping. Regards Viswanathan
how you taken aotitude test
how many earthing required for ups, what should be the earth voltages
Where the excitation is given either stator or rotor in actually in power plants?
How to calculate the input cable rating for 10kva ups (3phase input and single phase output and also 3phase output, battery rating 65Ah)provide the formula also.thnx
What is self exciting?
ro plant grundfos bm30type pump.we start the pump using siemens 3rw 4423-1bc44, 30kw soft starter. bur its failier frequently. so we planed to change the dol starter. sp please tell me any budy its possible or not翿შ†
why dc source used for HV breakers and Relays operation?
why we used stone chips under the transformer area..
is it possible to run the any motor when winding grounded? how?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)