how to connect 3 wire 4-20 mA transmitter in Plc system PLC
system and how explain how the measuring data communicate
with plc system.
We normally use a clean separate power source to power all
the instrumentation on the plant including the DCS and
PLC's. This instrumentation power source is going through a
UPS and a inverter backup system to smooth and minimize
power failures. Each zone in the plant normally have its own
24VDC power supply unit, but they are all backed up by the
same UPS.
The UPS can normally keep the instrumentation and other
emergency and critical power for about 6 hours in case of a
total main power failure.
In your 3 wire system the supply to your TX will be from
this external power source, and the loop power for your 4 to
20 ma will be generated by the same TX and will not come
from the PLC or DCS as with a loop power 2-wire systems.
Since the external power to your TX is the same as the 24VDC
power it generates for the signal, you can use the negative
as a common. This common(OV) and the 4 to 20mA(24VDC) signal
is then connected to the PLC as for a normal 2-wire loop
powered TX.
This common from your TX is 0V and is the same as the 0V of
the PLC or DCS since they are all from the same UPS.
The PLC or DCS will only get the positive of your TX as the
input signal, since all the negatives of the inputs are all
connected together on a common 0V bar close to the the PLC
or DCS and only one wire from this negatives bar is then
daisy chained to each input. The negative from your TX you
therefore also need to connect to this common negative bar
of the PLC or DCS and only the positive goes to the input
connection.
The only thing you need to remember is that the 3 and 4 wire
systems are externally powered systems and are therefore
active inputs or source inputs and that the loop powered 2
wire system is a passive or sink type input. This you then
need to set up inside the PLC or DCS input configuration
parameters.
Good luck
Is This Answer Correct ? | 13 Yes | 3 No |
How a rtd work, and what volts/current goes to a RTD to measure the resistence?
how to wire from pressure transmitter to marshalling panel and panel to controller and controller to dcs plz give the answer with example .
Is it possible to convert 4 wire transmitter to convert to 2 wire with additional relay.Please send detial with drawing,i will appreciate.
I have seen the Temperature element (T/C & RTD) installed in process line on 45 degree position, Why? What it mean? How many types of tapping position for temperature elements?
How can I read the electrical drawing easily?
what is difference between RTD and Thermocouple?
what is the calibration standard for pressure and differential pressure transmitters?
I want measure the volumetric flow of gas in waste heat recovery Boiler?Tell me how and which type of instruments required. Plz mail me:naba02222@gmail.com Sam please post the answer .
1.Give example of analog and digital signal 2. What is yhe advantage of 8086 than 8085
5 Answers Bhel, College School Exams Tests, Profitec,
why use 4-20mA in the field of instrumentation?
how can we calibate ph meter. how can we calibrat conductivimeter how can we calibrat massflowmeter & it s working.
what is Least Value of MICROMETER?