Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to connect 3 wire 4-20 mA transmitter in Plc system PLC
system and how explain how the measuring data communicate
with plc system.



how to connect 3 wire 4-20 mA transmitter in Plc system PLC system and how explain how the measuri..

Answer / sam

We normally use a clean separate power source to power all
the instrumentation on the plant including the DCS and
PLC's. This instrumentation power source is going through a
UPS and a inverter backup system to smooth and minimize
power failures. Each zone in the plant normally have its own
24VDC power supply unit, but they are all backed up by the
same UPS.
The UPS can normally keep the instrumentation and other
emergency and critical power for about 6 hours in case of a
total main power failure.

In your 3 wire system the supply to your TX will be from
this external power source, and the loop power for your 4 to
20 ma will be generated by the same TX and will not come
from the PLC or DCS as with a loop power 2-wire systems.
Since the external power to your TX is the same as the 24VDC
power it generates for the signal, you can use the negative
as a common. This common(OV) and the 4 to 20mA(24VDC) signal
is then connected to the PLC as for a normal 2-wire loop
powered TX.
This common from your TX is 0V and is the same as the 0V of
the PLC or DCS since they are all from the same UPS.

The PLC or DCS will only get the positive of your TX as the
input signal, since all the negatives of the inputs are all
connected together on a common 0V bar close to the the PLC
or DCS and only one wire from this negatives bar is then
daisy chained to each input. The negative from your TX you
therefore also need to connect to this common negative bar
of the PLC or DCS and only the positive goes to the input
connection.
The only thing you need to remember is that the 3 and 4 wire
systems are externally powered systems and are therefore
active inputs or source inputs and that the loop powered 2
wire system is a passive or sink type input. This you then
need to set up inside the PLC or DCS input configuration
parameters.
Good luck

Is This Answer Correct ?    13 Yes 3 No

Post New Answer

More Instrumentation Interview Questions

What is mean by SMART in an Instrumentation. is any full form for SMART?

3 Answers  


can anyone can let me know in Eurotron Micro cal 2+ calibrator in milli amps source mode we are not able to get 20 milli amps output it only produces 1.52 milli amps out, but display shows increase in milli amps , and err6 displays, let me know how to remove the err 6.

0 Answers  


What different types of problems do occur while doing the loop checking? and please explain in detail or mail me at kadam.aniket143@gmail.com

1 Answers   Operational Energy Group, Process Control Technologies,


why we take 4 to 20 mA as out put of every instrument like pressure transmittre ?why we cant take 0 to 20mA as output?

6 Answers   OGDCL,


We have ZR22G-100-S-A-E-T-T--E-A/CV/F1 Model Zirconia Oxygen analyser which is Yokogawa make. I kept the analyser in Flue gas path at Air pre heater area. My plant is 7.5MW Biomass power plant. For a particular fuel, Coconut Husk which contains Sodium and Potassium chlorides iam not getting proper reading, Analyser output always Zero. I calibrated the analyser and it is OK. For Other fuels like Wood chips, Cholam waste, DOB, Groundnutshells, Ply wood waste and all iam getting actual percentage of Oxygen. What is the main reason behind this draw back?

2 Answers  


what are the possible reasons if a control valve fails to open/close?

1 Answers   DEWA,


What is the difference between modbus,fieldbus & profibus

0 Answers   NSL,


For a diafhram 1.5 d =kn(p-p0) D4 Where d in deflection in inch k=constant n=no of capdule (P-P0)=Applied pressure in psi D In active dia at capsule. -1.5 d=k to p d being constant -1.5

0 Answers   L&T, Shiv Tech Marine Control,


How many types of Control Modes in process control, plz tell me all.....?

2 Answers  


what is the diffirence between Earth and Neutral

4 Answers  


what is the T/C & RTD mesuremaint?

3 Answers  


GIVE BRIEF DESCRIPTION ABOUT "DCS"

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)