what does happen if generator frequency fall in running
condition & what should require immediately
Answers were Sorted based on User's Feedback
Answer / kailash
Either we have to reduce load or we have to increase speed
of prime mover by increasing fuel (diesel/steam) through
governor.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / poorna
if the generator frequency falls during running condition
it may result in circulating currents if it running in
parallel with other generators or it is connected to grid,
remedy is to increase the speed of prime mover by any means
if not possible reduce the load
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / siva rao
the emf induced in alternator will reduced to very low value
and the generator will not serve any load.if the frequency
will fall to a lower value the excitation of the generator
must be increased.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / mahi&junu
there are two methods. Either we can decrease the load connected or we can increase the excitation
Is This Answer Correct ? | 5 Yes | 3 No |
What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer?
how many power plants in andhra pradesh,how many types and there capacity
What is the difference between isolators and electrical circuit breakers? What is bus-bar?
How can we calculate the KVA rating of a Distribution transformer from its core details?
anyone please send transformer parameter design formulas & details of tap changer ? plz i have interview this week its more helpful for me ?
how starting current in motor is reduced in case of motor in star connection.
i want to know about torque of slip ring induction motor
What is AVR in Generators and How is it working.
how gen. load increase or decrease ? what happen with gen on that time
how many hvdc lines in india???
In case of delta/delta transformer if the one phase is blown out then what will be secondary line voltage ?
What is Plank's Law?