what does happen if generator frequency fall in running
condition & what should require immediately
Answers were Sorted based on User's Feedback
Answer / kailash
Either we have to reduce load or we have to increase speed
of prime mover by increasing fuel (diesel/steam) through
governor.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / poorna
if the generator frequency falls during running condition
it may result in circulating currents if it running in
parallel with other generators or it is connected to grid,
remedy is to increase the speed of prime mover by any means
if not possible reduce the load
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / siva rao
the emf induced in alternator will reduced to very low value
and the generator will not serve any load.if the frequency
will fall to a lower value the excitation of the generator
must be increased.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / mahi&junu
there are two methods. Either we can decrease the load connected or we can increase the excitation
| Is This Answer Correct ? | 5 Yes | 3 No |
What is the difference b/w fanuc alpha series 16i and 18i controller. what is stand for i
what & how to check the lightning arrester
If two hack saw blades, seperated by 1mm thick paper,are connected across 230volts, and immersed in water,then they start getting heat. This is fact,i dont know how they get heated.Blades are not directly connected together. Please if anybody knows the fact ,revert back to me
what happens when dc supply is given to the transformer?
why induction motors are rated at 0.8 power factor.
State the difference between Three winding transformers and Two winding transformers ? where its used?
How we connect capacitors in Fixed Series compensation of AC transmission lines. Whether in parallel or in series?
what is the role of MPU in DG set
1 Answers Weltech Engineering,
Why CTs are connected in star on T/F delta connected winding side & in delta on T/F star connected winding side for T/F differential protection?
through which medium return supply given to alternator please answer in details
why the measure taken in multiplication factor of 11for voltage like.. 110V,220V,440V,1.1KV,6.6KV,11KV,33KV,66KV,110KV,132KV,220KV
what is the ambient temperature of transformer oil & winding?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)