can a motor acts as a generator
Answers were Sorted based on User's Feedback
Answer / suresh
motor has a stator and rotor.
if the rotor speed is above the synchronous speed it act as
a generator
| Is This Answer Correct ? | 23 Yes | 1 No |
Answer / dilip
if it is induction motor, then its rotor speed should be
greater that the RMF's Speed=Ns.
it should be noted that it will draw reactive component of
power for exciting it self.
| Is This Answer Correct ? | 4 Yes | 0 No |
motor has a stator and rotor.
if the rotor speed is above the synchronous speed it act as
a generator
if it is dc moor, then if you change the supply then it act
as generator
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / khushalchand
Only a Double excited Electrical machine can act as a
Generator. Please note eg. you cannot generate power from a
squirel cage induction motor as it does not have a dual
power source, it can only operate as a motor as the rotor
is short ckted. In all other cases where the stator
(winding) and rotors(armature) are powered seperately, only
then energy can be converted from mechanical to electrical
(generator) or electrical to mechanical (Motor)
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / dilip
if it is induction motor, then its rotor speed should be
greater that the RMF's Speed=Ns.
it should be noted that it will draw reactive component of
power for exciting it self.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / taufic
If we are using DC motor. We can DC motor act as Dg set
with combine primemover.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / p.senthil kumar
motor acts like generator for a short period of time when
it was stopped by removing input supply;this is called
regeneration. This regeneration EMF can be used for motor
braking systems in industries.
| Is This Answer Correct ? | 1 Yes | 1 No |
What will happen if 40W and 60W Bulb is Connected in Series.
What is distance between electrical panel to land ?
when we put inducter in neuteral grounding of genrator.
I completed iti in2004 I was worked in A grade contractor can I get c licence
how to select correct size of power cable for inverter duty motor
What is meant by short-pitched winding?
HOW TO CALCULATE THE HEAT AND LOAD OF LT-SUBSTATION WHICH CONTAINS 2*1MVA TRANSFORMERS,LT-SWITCH BOARD,MLDB,ACB,BUSBAR,ETC,......?
what happens if power factor is maintained at 0.9?give me the answer in technicall way rather than telling the penality n all
what r the types of detectors? state the location these detectors?
What is the difference between a fuse and a breaker?
why transformer ratings are taken in 11kv 22kv 33kv but not in 10,20,30kv
what is the best method of grounding in 30 MW generator?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)