why capacitor bank always connected in delta,why not in
star to a system?
Answers were Sorted based on User's Feedback
Answer / kk
Delta connection is parallel effective and star is series
effective. Capacitors offer more impedence when connected
in parallelthan in series.
Is This Answer Correct ? | 114 Yes | 21 No |
Answer / roysayan01
The reasons are-
1) The equivalent capacitance of a delta bank is more than
the equivalent capacitance of a series capacitor bank and so
more the capacitance more the reactive power will it supply
& since capacitor bank's sole purpose is to supply reactive
power, delta connection will serve better.
2) If there is any circulating current in the bank then in
delta this circulating current remains within the bank &
dont get spread to whole system unlike in star connection.
(for easy remembrance- due to the triangle shape of delta
connection circulating current circulates within the
triangle only)
3)In delta, phase current=line current/1.732
i.e the phase current becomes smaller and thus the losses
also decreases.
If ny1 disagrees or ve ny other questions do feel free to
mail me at roysayan01@gmail.com. I may be late in replying
but I will reply for sure.
Is This Answer Correct ? | 90 Yes | 10 No |
Answer / debasish
Capacitor is used to balance the line inductance and hence
to increase the power factor. The effective capacitive
reactance is 3 times more when connected in parallel than in
series. So, to improve the p.f. by a fixed amount, the
capacitance required in parallel is 1/3 of capacitance
required in series. So, the cost is less for parallel
connection.
Is This Answer Correct ? | 82 Yes | 9 No |
Answer / prashant
delta connection always give 3 time more reactive power than
star connection for same rating 'c 'of capacitor
Is This Answer Correct ? | 31 Yes | 8 No |
Answer / arvind
dear kk,
as per u capacitor offer more impedence it means resistance
and reactance will increase as per this equation
Z=(R+jX)^1/2.Then what is the advantage of having high
impedance in a system,
secondly, can u put more exaplanation on:-
Delta connection is parallel effective and star is series
effective?
Is This Answer Correct ? | 17 Yes | 9 No |
Answer / arvind kumawat
in the Delta connection, the phase voltage is equal to line
voltage, and in the star Connection it is 1.732 times.
The Delta Connection is Parallel wher star is series.
And the Capacitor Bank is Connected for the Power Factor
Improvement. so when connected in Delta Connection, the
Power factor can be Improved by a fixed amount.
THIS IS AS PER MY KNOWLEDGE............
ARVIND KUMAWAT
Is This Answer Correct ? | 21 Yes | 13 No |
Answer / madhu
c is capacitor connected.
In delta connecton,
source 3ph grounded star,
Q(per phase)=(omega)*(3*c)*V^2
In star connecton,
source 3ph grounded star,
Q(per phase)=(omega)*(c)*V^2.
so with low value of c we are able to supply more reactive
power in delta than in star.
Is This Answer Correct ? | 9 Yes | 8 No |
Answer / abhishek
capacitor is 1/wc. so if we parallaly add it is in series
and if we seriely add it is in parallel.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / atif anwar
As we all are familiar that equivalent capacitance of a delta bank is more than the equivalent capacitance of a series capacitor bank and so
more the capacitance = more the reactive power it supply
&
since capacitor bank's mere purpose is to supply reactive
power, delta connection will serve better.
it wld be more clear with expression:-
In delta, phase current=line current/1.732
capacitance required in parallel is 1/3 of capacitance
required in series
The effective capacitive
reactance is 3 times more when connected in parallel than in
series. So, to improve the p.f.
Is This Answer Correct ? | 2 Yes | 3 No |
how the rotating magnetic fieldis produced in induction machines??? give the correct explanation.is there any mathematical expression for the same?
What is the current carrying capacity of 0SWG,3SWG,10 & 12 SWG solid bare overhead copper conductors?
what is star&delta connections?
A dc motor running on dc drive whose input is 3ph AC what will happen if we change the phase sequence of dc drive for e.g (R Y B) is connect as R B Y, will the motor run as same as previously running before changing phase without any effect
How to calculate the NGR value for a 2.7MVA Transfomer, 11KV system where the fault current has to be limited to 50A?
For backup batteries connection,which method is best? series or parallel ?
How do we arrive at selecting reactive capacitance value as 30% of h.p rating of motor?
what is W.T?specify the acceptable range?
what is wave trap? And how it works?
How to calculate u.p.s load parsentage plz give me formula
does the transmission line model also requier active power in no-load operation?
Don't you have similar question banks related to Oral Certification Examination conducted by Mercantile Marine Departments / Directorate of Shipping, Ministry of Shipping for Electro Technical Officer?
0 Answers Bernhard Schulte Shipmanagement,