Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why capacitor bank always connected in delta,why not in
star to a system?

Answers were Sorted based on User's Feedback



why capacitor bank always connected in delta,why not in star to a system?..

Answer / kk

Delta connection is parallel effective and star is series
effective. Capacitors offer more impedence when connected
in parallelthan in series.

Is This Answer Correct ?    114 Yes 21 No

why capacitor bank always connected in delta,why not in star to a system?..

Answer / roysayan01

The reasons are-
1) The equivalent capacitance of a delta bank is more than
the equivalent capacitance of a series capacitor bank and so
more the capacitance more the reactive power will it supply
& since capacitor bank's sole purpose is to supply reactive
power, delta connection will serve better.
2) If there is any circulating current in the bank then in
delta this circulating current remains within the bank &
dont get spread to whole system unlike in star connection.
(for easy remembrance- due to the triangle shape of delta
connection circulating current circulates within the
triangle only)
3)In delta, phase current=line current/1.732
i.e the phase current becomes smaller and thus the losses
also decreases.

If ny1 disagrees or ve ny other questions do feel free to
mail me at roysayan01@gmail.com. I may be late in replying
but I will reply for sure.

Is This Answer Correct ?    90 Yes 10 No

why capacitor bank always connected in delta,why not in star to a system?..

Answer / debasish

Capacitor is used to balance the line inductance and hence
to increase the power factor. The effective capacitive
reactance is 3 times more when connected in parallel than in
series. So, to improve the p.f. by a fixed amount, the
capacitance required in parallel is 1/3 of capacitance
required in series. So, the cost is less for parallel
connection.

Is This Answer Correct ?    82 Yes 9 No

why capacitor bank always connected in delta,why not in star to a system?..

Answer / prashant

delta connection always give 3 time more reactive power than
star connection for same rating 'c 'of capacitor

Is This Answer Correct ?    31 Yes 8 No

why capacitor bank always connected in delta,why not in star to a system?..

Answer / arvind

dear kk,
as per u capacitor offer more impedence it means resistance
and reactance will increase as per this equation
Z=(R+jX)^1/2.Then what is the advantage of having high
impedance in a system,
secondly, can u put more exaplanation on:-
Delta connection is parallel effective and star is series
effective?

Is This Answer Correct ?    17 Yes 9 No

why capacitor bank always connected in delta,why not in star to a system?..

Answer / arvind kumawat

in the Delta connection, the phase voltage is equal to line
voltage, and in the star Connection it is 1.732 times.
The Delta Connection is Parallel wher star is series.
And the Capacitor Bank is Connected for the Power Factor
Improvement. so when connected in Delta Connection, the
Power factor can be Improved by a fixed amount.
THIS IS AS PER MY KNOWLEDGE............
ARVIND KUMAWAT

Is This Answer Correct ?    21 Yes 13 No

why capacitor bank always connected in delta,why not in star to a system?..

Answer / erbhavin_patel

i have no idea

Is This Answer Correct ?    19 Yes 13 No

why capacitor bank always connected in delta,why not in star to a system?..

Answer / madhu

c is capacitor connected.
In delta connecton,
source 3ph grounded star,
Q(per phase)=(omega)*(3*c)*V^2

In star connecton,
source 3ph grounded star,
Q(per phase)=(omega)*(c)*V^2.

so with low value of c we are able to supply more reactive
power in delta than in star.

Is This Answer Correct ?    9 Yes 8 No

why capacitor bank always connected in delta,why not in star to a system?..

Answer / abhishek

capacitor is 1/wc. so if we parallaly add it is in series
and if we seriely add it is in parallel.

Is This Answer Correct ?    0 Yes 1 No

why capacitor bank always connected in delta,why not in star to a system?..

Answer / atif anwar

As we all are familiar that equivalent capacitance of a delta bank is more than the equivalent capacitance of a series capacitor bank and so
more the capacitance = more the reactive power it supply
&
since capacitor bank's mere purpose is to supply reactive
power, delta connection will serve better.

it wld be more clear with expression:-
In delta, phase current=line current/1.732
capacitance required in parallel is 1/3 of capacitance
required in series

The effective capacitive
reactance is 3 times more when connected in parallel than in
series. So, to improve the p.f.

Is This Answer Correct ?    2 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

as per IE stranded what is max voltage between neutral to earth. 100 kva transformer neutral solid earth. min and max values i need to ans for RTI question

2 Answers  


Why control of DC motor is simpler?

0 Answers   BARC,


Following test should be conducted to find out relative polarity of transformenr terminals A no load test B back to back test C phasing out test D none of above

0 Answers  


why the neutral line is not giving shock to us if we touch it ?

0 Answers   GPREC,


what is the best way to start a 15 KW motor for pump star-delta or direct on line ? and from how many KW i must use direct on line ?

1 Answers  


what is servomechanism?

1 Answers  


i completed my b.tee(eee) in 2009, but i did not join any job, i joined in my father business, now i want to join any good job, please suggest any course for me

1 Answers  


How stabilizer works

1 Answers  


What is meant by unilitrel device?plz tell about h-parametrs

1 Answers  


i want to run 11kv star connected motor in 6.6kv with delta connected throught inverter, is it possible?

0 Answers  


How much load with stand the copper cable by sq mm apro..

1 Answers   L&T, Taj Group,


what is the difference between OSR and BUCHHOLZ relay of transformer?

1 Answers   Bhushan Power Steel,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)