What is the voltage b/w nutral and earth
Answers were Sorted based on User's Feedback
Answer / irfan hussain memon
in balanced condition both neutral and earth has 0
potentional voltage.
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / bhavneet kumar surya roshni lt
Should be less than 2volt for
low load.
And for heavy load less than
5volt.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / shaddan shahjahanpuri
न्यूट्रल और अर्थ के बीच वोल्टेज 0 वोल्ट होता है
यदि लोड सन्तुलित है
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / sreekumar
earth to nutral voltage depends on the impedence of the
winding of transformer(distribution transformer) for normal
case there is a small current flowing through the nutral to
earth because of the unbalance in phase voltage/current.it
depends on the impdence of winding.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / om
earth is a refference voltage and assuming as a zero voltage
while nutral is commone point of any ckt or network it may
be zero or any value so it may be zero or may not be zero
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / parvesh1989
0.001 OHM,
because when a body is earth, its attains a zero potential
or potential of earth.
Another answer is 0 to 4 volt properly.
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / kravi
Good earth voltage is zero
for bad earth is .......
Is This Answer Correct ? | 2 Yes | 7 No |
why the air gap is necessary in the transformer core
How to calculate incomer of a capacitor bank/feeder from its KVAR, AND how to calculate the copper busbar for rated incomer,like for 400A we calculate the 40x10 of aluminum busbar.
how many safety really of DG sets.
What are safety seals?
If the output of a 100kva, 415v generator is stepped up to 11kv with a 500kva transformer,can the transformer be Loaded above the source generator loading?
In LRS how much water PH value maintain for good operation of motor?
Explain what is use of lockout relay in ht voltage?
If DC supply is given to a transformer it may a) Work b)Not Work c)Give lower voltage than the rated voltage on secondary side. d)burn the winding
installation of subsatation of33kv
Why the suply frequency in INDIA is 50HZ
How many earthings are required for motors?
what is the meaning of number in (11, 31, 61,14, etc. CDG11, CDG31, CDG61, DDT32