Answer / kumar.latif
it is the ratio of total voltage capacity of a scr string
to sum of capacities of individual scrs.
If V is total capacity and v is individual thyristor
capacity then derating factor=V/(nv) where n is the no of
thyristors
Is This Answer Correct ? | 23 Yes | 15 No |
Answer / saroj kumar
String Efficiency=Actual Voltage or Current/n* Individual Voltage or current.
Derating Factor= 1- String Efficiency
=1-V/n*v
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / nhatanael
how to determine number of thyristors in series. in hvdc valve converter.
to determine derating factor you first need to know number of thyristors connected in series...
Is This Answer Correct ? | 0 Yes | 0 No |
difference between ac and dc generators
what is the formula for converting KW into KWH ?
how to calculate differential current when we testing differential relay..suppose we have 1000kw generator,630amp VCB,what value we should put /inject so that relay trip the VCB? PLLZ justify ur comment
3 ph motor connected in star delta starter. when we start the motor it run in star but when in is going in delta it trips the main incoming supply. why?
whatare the disadvantages occur,if the form factor of transmission will not be equal to 1.11
What is the power rate of power transformer?
wht is meant by sh6
If we impress a dc voltage of 230 V on an unloaded 230 V, 50 Hz transformer it wi A give high secondary voltage B burn out C give secondary voltage as per K D none of these
how electricity is generated an supplied till consumer
what type of motor are there in megger how they work.
How open delta used for protection?