why neutral grounding transformer is used for generator and
why it is not used for transformers?
Answers were Sorted based on User's Feedback
Answer / tanvir s.
As far as i understand Neutral Grounding Transformer are used to Ground the both transformers as well as Generators. NGT is applicable (useful) in transformers/generators with delta connection. So during line-to-earth faults, the NGT helps the zero sequence current to flow in the ground. Any unbalance in the load distribution between the three phases is passed thru the neutral, which is not available in case of delta connection. Hence the NGT.
| Is This Answer Correct ? | 9 Yes | 4 No |
Answer / sunil kumar sinha
Neutral grounding transformer is used to limit earthfault
currentof generator. It also provide Generator earthfault
protection, both alarm and trippingby connecting voltage
relay across the secondary winding of NGT.
| Is This Answer Correct ? | 4 Yes | 1 No |
why some transmission lines have 7 wires n why some have 3 n 4??
Suppose a 3 phase, 2 pole, 440V induction motor is driving a flywheel of 600mm diameter, 150kg mass. By using v-belt and pulley, the speed is increased to 4500 RPM. What will be the effect on motor current?
what r the safety measures in UPS ? explain all?
What is R/X ratio? I have heard that this ratio is higher in a radial distribution system.Why is it so? I would appreciate a word. Thank you
1 Answers Power Grid, Vignan University,
why white color LED light is not possible?
what is B , c & d curves in MCB characteristics i e Full Form of B , C & D . sir please give me answer
for 24000kv transformer what is the value earthing resistence?
why name plate detail HP/KW rating of a motor is different from measured value HP/KW using formula?
what is reactive power and active power
what is pf. how to calculate capacitor bank value to maintain unity pf.
18 Answers JH, Saint Gobain, Supreme Treves,
Determine the MVA rating of the power transformer given that 110/66 kV,1000 Amps. Folks how can i calculate the MVA rating with this Data??Plz Help........
why the value of impedence is taken as %impedence in fault currrent calculation
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)