how much capacity(rating) of generator required to operate a
load of 100kv.
Answers were Sorted based on User's Feedback
Answer / shashidara reddy
rating purely depends on load not on vltg.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / abhishek jha
rating depends on wattage rating and not on volts. also if
it is 100 kw then if its power factor is assumed to be 0.8
then to supply that load ganerator rating should be
100/.8=125
| Is This Answer Correct ? | 1 Yes | 0 No |
How much the fault level of 11 k.v.,22 k.v., 33 k.v. (in Maharashtra- M.S.E.D.C.L) for calculation of short circuit current & selection of h.t.cable.
What are the section criteria for cables. Now everywhere XLPE power cable is used or PVC is also used?.
how to find the capacitance value of the motor while running??
Why secondary of a CT in a power system acts as an open circuit after core saturation?
3.7 kw motor ,how much sq mm cabel want to bare this motor load
what are the values of VRY,VYB,VBR,Vry,Vyb,Vbr,Vrn,Vyn,Vbn for Magenetic balance test of 100 KVA and 63 KVA Distribution transformer
lightning current is ac or dc..?????
What is the difference between ELCB and RCD
Why we are testing a tan delta test in transformer? which purpose conduting that test? and time priode test?
WHWT IS USE OF VACCUM CIRCUIT BREAKER
what is the full load current and power rating of 1 Tonne Air Conditioner?How will Calculate?
What is the type of earth fault protection used in battery? explain.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)