what is the difference between mmhg & mmwc?. i want to
calibrate a transmitter in the range of -100 to 300 mmwc.
Which is the reference for calibrate the Tx,if mmwc not
available?. Is it mmhg or mmho2?.

Answers were Sorted based on User's Feedback



what is the difference between mmhg & mmwc?. i want to calibrate a transmitter in the range of..

Answer / sam

Hi there,

mmwc (millimeters Water Column or Water Gauge)
mmH2O milimeters water)

Let me explain the pressure value of each since I can see
you have asked the same question earlier as well.

We all know that the gravitational acceleration of the earth
is 9.80665 m/s2 as a accepted standard around the world.
Our pressure system was also derived from this Universal Law
of Gravitation first developed by Sir Isaac Newton.
I think we all heard the story about Newton sitting under an
apple tree, an apple fell on his head, and he suddenly
thought of the Universal Law of Gravitation.
Anyway long story short, memorize the following formula and
you will not ever get confused again about pressures and levels.
1 meter height of any volume of clean water (1mWC) is equal
to 9,81Kpa. That is the true and accurate pressure value of
1meter height of water, regardless if it is in a small
tubing or the swimming pool or the ocean or the measured
height in the vessel you want to do a level calibration on.
a 1 meter height of clean water is always 9,81 Kpa.
Ok I know still a bit confusing.

Due to the above information we can therefore say 1000mm of
Water Column is = to 1000mm Water = 9,81Kpa or
1000mmWC = 1000mmH2O = 9,81Kpa

Now we all know the formula to calculate the calibrated zero
and span of our transmitters,
sg x g x h = Kpa

So for a vessel with a zero to span distance of 1000mm and a
product sg value of 1(clean water) we can do the calculation.
1 x 9,81 x 1 = 9,81Kpa
or if you want to work only in mmH2O,
sg x h = mmH2O
1 x 1000 = 1000mmH2O
So now you can calibrate your transmitter for the above
example for LRV = 0Kpa and URV = 9,81Kpa or if you set the
UOM on the transmitter to mmH20, you can calibrate it for
LRV = 0mmH2O and URV = 1000mmH20.
If the height or the sg value in your application differs
just substitute your values in the formulas and you will be
able to do any level calibration on any PIPED DP transmitter.
Remember these formulas are only for piped DP transmitters
and not for capillary or wet leg applications.

Ok let's move on to:
mmhg (millimeters mercury)

This UOM is normally used the measure vacuum and 1
atmosphere = 760mmHg.
You can also say 0mmHg = -101,3Kpa(a) since 1 atmosphere =
101,3Kpa. The (a) indicates that we are talking about
absolute pressure and not gauge pressure.

If you really want to confuse yourself you can try and
relate what I have said above in the mmH2O example, to mmHg.
You can say that 1000mmH2O = 73,56mmHg.
Forget about mmHg and don't use it, not even when you work
on vacuum applications. Stick to Kpa or PSI or the UOM that
makes sense to you and what you are use to. All the UOM are
very easy to convert to so always first convert the
measurement to units you are familiar with then start your
calculations.
Personally I only work in Kpa and mmH2O and I don't get
confused at all anymore.

So finally if you want to do you calibration as per your
question and you are SURE that the calibration is right, set
you UOM on your transmitter to mmH2O and set the LRV to
-100mmH2O and the URV to 300mmH2O and put it back on line.

If you do not use a SMART transmitter convert your
calibration values to Kpa or PSI and pump your transmitter
up to these values and set the zero and span accordingly.
-100mmwc to 300mmwc is the same as 0 to 400mmwc so if your
transmitter cannot measure in the negative you can set the
calibration for 0 to 400mmwc as well, just make sure the
zero is good at atmospheric presure.

Is This Answer Correct ?    35 Yes 5 No

what is the difference between mmhg & mmwc?. i want to calibrate a transmitter in the range of..

Answer / nileshji sekar saudi kayan

I DONT WANNA MAKE BIG STORY LIKE SAM
760mmhg = 10000mmwc = 10000mmh2o
apply pressure on txmtr hp side = -100mmwc or -7.6 MMHG=4mA
(IF NOT GETTING 4 MA DO ZERO TRIM)
-100mmwc or -7.6 MMHG =4mA
0 MMWC OR 0 MMHG = 8 mA
100MMWC OR 7.6 MMHG =12 mA
200MMWC OR 15.2 MMHG =16 MA
300MMWC OR 22.8 MMHG = 20 MA
(IF NOT GETTING 20MA DO UPPERSENSOR TRIM
MAKE SURE WHILE U APPLYING PRESSURE LP SIDE OF TXMTR IS
OPENLY VENTED TO ATMOSPHERE

Is This Answer Correct ?    11 Yes 3 No

what is the difference between mmhg & mmwc?. i want to calibrate a transmitter in the range of..

Answer / santhu

hi sam, i am suffering from same question? Now i got exact
explanation from you? Thanku for post answer?after seeing
your answer... i have some other doubts on instrumentation?
i want share my doubts with you if u interest to face my
questions please give me ur mail id? my mail id is
msanthu.power@gmail.com

Is This Answer Correct ?    2 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

Transducer Input 0 to 230 v ac Output-0 to 10vdc Receiver Input 0 to 10 vdc and Output 4 to 20 ma How?

1 Answers  


Linear amplifier.

0 Answers   CCIE,


suppose there is gas flow meter I want to know weather meter calibration is done at high pressure or low pressure? pls justify.

2 Answers   Siemens,


what is orifice plate? Give me best answer?....plz

5 Answers  


What is Hysteresis mean in Instrument?

11 Answers  






1. For Steam drum level signal, why do we compensate with drum pressure signal? 2.For main steam Flow signal is comensated with main steam temperature signal and main steam pressure signal why?

0 Answers  


Describe the function of Accumulator into the Pump

0 Answers  


How do we MEASURE OR CALCULATE VELOCITY used to calculate REYNOLDS NUMBER??

3 Answers  


wht is snap action switch?where it is used?is there any diff between snap action switch and normal pressure switch?

1 Answers   ONGC,


what is sliding spool valves?

0 Answers  


Working principle of magnetic flow meter ......and calibration procedure of e+h magnetic flowmeter...

0 Answers  


What is frequency factor in massflow meter? When using frequency output?

0 Answers   PCMIL,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)