when voltage increases then current also increases then what is
the need of over voltage relay and over current relay?
can we measure over voltage and over current by measuring current
only?
Answer / nithi
NO.We can't sense the over voltage by just measuring the
current only.because,
The current increases not only for over voltages but
also for under voltage(As most of the loads are non-linear
in nature).
So,the over voltage protection & over current
protection are completely different.
over voltage relay meant for sensing over voltages &
protect the system from insulation break down and firing.
over current relay meant for sensing any internal
short circuit,over load condition ,earth fault thereby
reducing the system failure & risk of fire.
So, for a better protection of the system,It should have
both over voltage & over current relay.
Is This Answer Correct ? | 15 Yes | 0 No |
how can i select the cable ratings
I have running 4 generator in paralel.All generators Voltages is same(470 V),KW also same (100 KW) but only No2 generator Amper is high than another generators. DG No:1,3,4 470V,100KW, 150 A DG No:2 470V,100KW,400 A
In winding design, the angle of chording (β) is nearly equal to A 45 degree B 60 degree C 30 degree D 90 degree
whats happen if we disconnect the NGR of alternator in running condition?. Generally we observed that transformer netrul is directly grounded but alternator connected with NGR, then ground?
What is maximum demand?How can we caluclate it?
transformer losses
model question paper for supervisor trainee
what is ACB and its function?
why, when birds sit on transmission lines or current wires doesn't get shock?
36 Answers College School Exams Tests, Infosys,
The specific heats of the gas at constant pressure and constant volume are respectively 1.0 kJ/kg K and 0.72 kJ/kg K; the value of R for the gas is
how to maintain frenquncy with syncronising sub-station for distribution
How to Calculate IKW(input kilowatt)of a Chiller plant