1. Why transfomer reting in KVA and Motor in HP..

Answer / venkat boyi

The rating of any electrical device is based on losses
developed in the machine.In Transformer the losses depends
up on only Voltage and current but not on PF, hence the
rating of it is in KVA. In motor the output is mechanical
and mechanical load represented by HP in Watts

Is This Answer Correct ?    44 Yes 2 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / sudhir singh

the rating of any machine depend the losses.The losses in
transformer which are iron and cupper losses depend upn the
current and voltage and not on their product so its rating
is in kva not in hp.
As motor gives mechanical output which is measured in hp.

Is This Answer Correct ?    16 Yes 1 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / sekar

for transformer we can connect any load(R,L).so its power
factor variable . so it is in kva...
since motor is a load .It is designed for particular power
factor.

Is This Answer Correct ?    5 Yes 1 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / h r jadhav

transformer handels electrical energy matching to the
system which containing active and reactive power .which
measured in volt amp capacity.hence rated as mva or kva.how
ever electric motor is meant for converting electrical
energy into mechanical energy that is shaft power . and
shaft power is always rated in horse power .

Is This Answer Correct ?    1 Yes 1 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / om prakash rai

in transformer only two losses is consider one core loss and
other copper loss and core load is depend on the voltage(v)
and copper load depend on the current(i),so we know the
rating of every system is dependent on his system loss so
transformer rating in KVA .in moter,the output of moter is
mechnical so its rating is always consider in HP.

Is This Answer Correct ?    1 Yes 1 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / sudhi

The rating of any electrical device is based on losses
developed in the machine.In Transformer the losses depends
up on only Voltage and current but not on PF, hence the
rating of it is in KVA. In motor the output is mechanical
and mechanical load represented by HP in Watts

Is This Answer Correct ?    1 Yes 1 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / chandresh

transformer losses depends on the load does not include power factor, motor include power factor

Is This Answer Correct ?    0 Yes 0 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / david wilson

By convention:
Power supplies are rated for their capacity to output power and are rated in VAs or kVAs.
Loads are rated for their power consumption and are rated in hp (In Europe they would be rated in Watts or KW as metric units).
For the purposes of ratings, transformers are rated based upon their ability to supply power to a load and so are rated in VA.
A 1kVA transformer can drive a motor of up to 1.34 hp (1kW).
Note: It the transformer was rated by the power it consumed (the losses when 1KW is drawn from the output) it would be more difficult to figure out what size of transformer you need to drive your 1.34hp motor.

Is This Answer Correct ?    0 Yes 0 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / yogee.basu

1.Transfomer is a balance load ,( trere is no change in
pf,frequnce, and load)
2.Motor is a un balance load (it is change in pf,frequnce,
and load)

Is This Answer Correct ?    16 Yes 26 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / gunasekaran

for transformer it is electrical load. but motor is
machanical load so it is HP transformer in VA

Is This Answer Correct ?    6 Yes 21 No

Post New Answer

More Electrical Engineering Interview Questions

I decided to provide a 11KV / 440V Xformer in my Substaion. What are the protection required for that?

5 Answers  


how to select DG set for certain load?

7 Answers   ACC,


What do you mean by PT-100?

8 Answers  


in the Distribution system .which one is Most Economically used by Power Engineer ? a)3 Phase3 wire System or b) 3Phase -4wire System

6 Answers   APTransco,


what is the working principle of smoke detector in fire alarm system

2 Answers   Vijaya Bank,






i have installed my solar site of 6.7kw and is working perfectly , can somebody tell me that how can i measure my solar irradiation kw/day/sq m ?

3 Answers  


What are the various types of BUSBAR Schemes? explain each

1 Answers   NTPC,


why we use star connection in HT motor? and delta connection in LT motor

2 Answers   npcc,


why dont we connect the two 12 V DC batteries in parallel, for an inverter (UPS)? is there any harm ?

6 Answers  


Thumb rule for capacitor bank calculation

1 Answers  


How we detect the leakage current of 11 KV H.T. motors and waht is the maximim limit?

3 Answers   Ambuja, Pristine,


What are the safety devices on Cumins Diesel Generators from 500 kva to 1500 kva.

1 Answers   Maruti Suzuki,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)