How to Convert horsepower to kva?
what is the three phase formula?
explain me if u can Example..i have 50Hp Moter how can i
convert in kva tell me formula three phases
Rehan Smileavail@msn.com
Answers were Sorted based on User's Feedback
1 L.Current xL.Volts x1.732 = KVA =
KW = HPX746
1000 PF
1000XEfficiencyxPF
2 L.Current xL.Volts x1.732XEfficiencyXPF =
KVAX1000XEfficiencyXPF = KWx 1000
xEfficiency = HP
746 746 746
When KVA know When KW know
When HP know
3 L.Current = KVAX1000 = KWx
1000 = HPX746
L.VoltsX1.732
L.VoltsX1.732XPF
LVoltageX1.732XEfficiencyXPF
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / shanker ganesh
first convert HP to KW (ie)1HP=0.75kw approx. from that u
can got KW valu then by using normal formula ie) kw=root 3
v i cos pi, u calculate KVA.
| Is This Answer Correct ? | 16 Yes | 11 No |
Answer / raghavendran
1 HP = 746 watts/motor designed PF = motor rating in KVA
for 50 HP motor = kva rating = 50 * 746/.85(say) = 44 KVA
| Is This Answer Correct ? | 13 Yes | 11 No |
Answer / edward
The automatic calculation hp to kva is in these pages:
http://www.calculatorsconversion.com/en/hp-to-kva-calculators-conversion/
Also
KVA, KW, KVA Conversion (http://ncalculators.com/electrical/kva-conversion.htm
| Is This Answer Correct ? | 0 Yes | 0 No |
If 24 KVA AVR having Input voltage 200-400v, Output voltage 415+-1%, what will be the voltage if Load is 13A.
the minimum clearance b/w ceiling and plane of leaf of ceilng fan shall be ..........mm
Why the standard of ambient teperature mentioned as 40 degree celcius in machines.
what is function and advantage of double delta winding in induction generator?
Why the stator is rotated in ceiling fans not Rator?
what is the difference between LLL and LLLG fault ?
Why DC exitation to AC Generator? Why not AC?
how to Select Lighting arrester? What r the parameters to be considered for the selection of Lighting arrester ?
If the Brush of DC motor is shifted by 90 deg, then what happens to voltage and torque? Both voltage and torque are zero. how to justify the answer?
electrical
Can a generator rated 400 V, 60 Hz be used in a 50 Hz System? Yes or No ? Why ?
my UPS suddenly goes off and all panel light also blow off.This happens even main electric supply is not interrupted.After some time it automatically starts functioning normally.Batteries are new.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)