Answer / dinesh lokhande
Transformer bushings OIP (Oil impregnated paper) consist of
paper foil surrounig conductor which termiantes at test tap
and oil is filled in between paper. This arrangement is
equivlent to no of capacitances in series.
To check healthiness of deielectric we conduct Capacitance
Tan detla test from specially designed apparatus which
gives values of capacitance and tan delta which can be
compared to Factory test results and designed values.
Vector disagram is as shown below.
Ia* *Ic
* *
* *
*D *
* *
**
*************** V
In above vector we can explian as follows.
From property of ideal capacitor currnet vector Ia leads
Voltage vector V by 90 deg.
However due to dielctric losses, Calculated or charging
current Ic lags behind actual current by angle delta (D -
dielctric loss angle).
Hence Tan delta calculated is dielectric loss.
Is This Answer Correct ? | 22 Yes | 5 No |
two 100W/230V bulb are connected in series. what would be the voltage drop across 1 bulb
On wat basis TSM & PSM are set? Example.TSM=30% n PSM=2.5A....Hw they are set and how we come to know that the particular relay should be set to this value only?
i have flexible wire. size of conductors is 0.190 mm & no.of conductors are 48. then size of wire comes 1.37 sqmm instead of 1.5 sqmm . the what is tolerance for this size.
HOW CAN YOU CALCULATE PRACTICAL EFFICIENCY OF A ASYNCHRONOUS INDUCTIONMOTOR OF 7.5KW,& MOTOR IS RUNNING WITH AVOLTAGE OF 410 VOLTS,& TAKING CURENT OF 13 AMPS
which type of effect of turbine and generator reverse power protection ?
The SFC of an engine is 0.25 kg/kW hr. when the fuel used has a calorific value of 36000 kJ/kg. the thermal efficiency of the engine is
why phase to phase voltage is 400v while phase to neutral is 220v?
if an insulated power and control cables of a running gas diesel gensets laid direct in an open trench i.e, trench bed is not rcc of a power house in which rain water, spillage water alwas exists and all power control cables remains submerged even when gas gensets of 480 kw each runningin on load. These power &control cables runs from power house to switchgear room through these trenches in which water remains most of the time. pl explain its merit & de-merit
is 3-phase induction motor need a starter ? why do it so
why motor burns ?
define reactive power?
how to calculate power loss cost of aluminium conductor and copper conductor?v=500v.i=100A.x-section area=68mm.squre conductor