Explain how you can give the overload setting to any Motor
Protection
Relay for a HT motors with formula and example?
Answers were Sorted based on User's Feedback
Motor current rating is calculated by using the formula
I= P/1.73*V*PF
Normany it is 1.8times of power of the motor will be their
in 420v 3 phase motor.
Ex: 500Kv HT motor 11kv voltage
is Approx. 32A is the rated current.
so 32.5 or 33A is OL Setting.
| Is This Answer Correct ? | 6 Yes | 3 No |
To attain a powerfactor more than .95, how much kvr should we use for 100 HP of current
4 Answers Bhel, Scooters India,
why we use star and delta connection?why we donot give the supply directly?
12 Answers Hitech, Siemens, Tata Steel Limited,
We have 3 Gensets 1.500kva,2.380kva,3.250kva How can we connect in common busbar&we have variable load.
Is the theorem applicable to ac sources?
what is the difference between earth and neutral.
what is mean by current
what are the sample questions asking to the test cunducting for electrical superwising lisence test?
In case of 3Phase Supply, Voltage R-Earth/Neutral - 220 Y-Earth/Neutral - 220 Z-Earth/Neutral - 220 Total is -> 660Volts Then Why it is said that 3Phase supply is 440
6 Answers Hindustan Unilever Limited,
what is the cable size we can use for 11kv and 33kv ?
What is the function of interposing current transformer?
What is the meaning of Fault level rating?
1 Answers Balrampur Chini Mill,
How do you determine the size of transformer radiators in a transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)