To attain a powerfactor more than .95, how much kvr should
we use for 100 HP of current
Answers were Sorted based on User's Feedback
Answer / r. thirumoorthy
I DON'T KNOW EXACTLY, ITS MAY BE CORRECT.
POWER FACTOR=KW/KVAR;
IN THIS CASE WE KNOW KW VALUE INDIRECTLY 1 HP=746 WATTS
SO 100 HP=74600 WATTS
AND POWER FACTOR=0.95
THEREFORE REQUIRED KVAR=74600/0.95=78526.315
IF IT IS WRONG SEND ME CORRECT ANSWER.............
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / s.arul
SOLUTION:
1 HP = 735.5 watts
100 HP = 73550 watts
KVA = KW/PF
KVA = 73.55/0.95
= 77.42 KVA
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / jm
SOLUTION:
1 HP = 735.5 watts
100 HP = 73550 watts
KVA = KW/PF
KVA = 73.55/0.95
= 77.42 KVA
this solution is wrong, this solution indicate the KVAR rating for that specific power factor, for example the power factor of your 100HP is .7, its the KVAR of .7 pf not the .95 becuase you need a KVAR in order to increase its power factor, compute it using power factor correction, and vector diagrams.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / k.prakashchandra
Depends on the present pf, however 30 KVAR is generally
recommended.
| Is This Answer Correct ? | 0 Yes | 2 No |
what is the location of lighting switch of battery room
two transformers of the same type, using the same grade of iron and conducting material, are designed to work at same flux and current densities, but the linear dimension of one are two times of the other in all respects. The ration of kVA of the two transformer closely equal to................? options: 16, 8, 4, 2
What are the causes of eddy current losses?
How does a star connection and delta connection work? How does the star connection save starting current and how does it change to delta?
When the load on the system is zero and Capacitor bank is on condition, is capacitor bank takes any load?
what will happen if 11KV is given to 1.5 square mm cable connected with constant load of 10A ?what will be the condition of cable after injecting the voltage?
What fomula is used to calculate: 1. rated frequency withstand voltage, and 2. rated lightning impulse withstand voltage.
How will polarity test of Dy5 transformer ?
why stator winding of synchronous machine are connected in star connection ?
What will happen if primary of transformer is fed with Square wave instead of sinsoidal wave ?Will it operate or Not?
can we start slipring motor on star delta like we start induction motor ? if yes where will we connect ?
what are the components in electrical control panel (for example: 415V, 3-ph, panel to operate utility and 3-ph DG set).
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)