what will happen if one of the phases from a 3-phase motor
is disconnected?? stop/run at 2/3rd speed or run at same
speed????
Answers were Sorted based on User's Feedback
Answer / niranjan
The motor will keep on running for a while but the current will rise on the other two phases and the overload relay will fall out, if its properly set and the motor will stop if the overload relay is set to high the motor will burn out
in the start Motor will start to shake the if there is no protection devices for over-load on the motor it will simple explode:)
Three-phase motors also vibrate less and hence last longer than single-phase motors of the same power used under the same conditions.
Is This Answer Correct ? | 5 Yes | 0 No |
Is there any local or International standards that prohibit the installation of earthing pit in the planters area where the earthing pit is subject to continues soak in water?
what is the calculation involved to design the heater to heat 10KL of water in temperature control unit?
What are the advantages of nichols chart?
how to calculate the watts from the tr
what is the general Classification of Generators
what is V=4.44FBN, THIS 4.44 ONLY U GOT the voltage in term sof 11, 22 etc this 4.44 u will get from form factor which has a value of 1.11
how to calculate the neautral earthing conductor size for a 500kva dg set.
What are the different condition monitoring techniques for a motor?
1)Why potential transformer primary site grounded? 2)can be loop between neutral & body for grounding? 3)What is the difference between ELCB &RCCB? 4)Why we use iron core in transformer insted of wooden core? 5)what is the principle of excitation? 6)Why we test the core balance test for transformer? 7)what is creepage?What is the creepage length for insulators at different voltages? 8)How much type of relays used for differential protection of generator,transformer & busbar protection?
What is the formula to find out two phase active & reactive power
when the PFR (POWER FACTOR REGULATOR)change a step to zero,one of the RCCB will triped off,is it the changing step of this PFR effect the RCCB?
how calculate gd2 of ht motors
0 Answers Hindustan Copper Limited,