which is batter in construction job,ELCB or RCCB?
Answers were Sorted based on User's Feedback
Answer / pramod r prakash
ELCB because it trips on any laekage of current within 30
milli amps.This helps in preventing shock and electrocution
owing to failure in insulation or short circuit.
Is This Answer Correct ? | 28 Yes | 7 No |
Answer / s.saravanan
--> RCCB is better than ELCB...
--> ELCBs senses the fault current flowing through the
ground only...
--> But fault currents can still flow through other
conducting elements such as an adjacent conductor which is
unenergized and whose insulation is incidently got damaged
and coming in contact with the conductor which is live and
its insulation also got damaged...
--> In this instant fault current flowing through the
ground is nil and the ELCB fails to sense it...
--> But RCCB works in core balancing technique and
therefore any difference in current flowing in through a
Line conductor and current flowing out of the neutral
conductor during faulty conditions will be sensed by the
detector coil and trips the circuit...
--> Let us widen our knowledge over the fault currents
since fault current doesn't flow only through ground but
also in some other unplanned paths...
--> Hope my answer will be more convincing to all...
--> All the best...
--> Have a nice day forever...
Is This Answer Correct ? | 13 Yes | 0 No |
Answer / vijay
There are two types of ELCB:
voltage operated and,
current operated.
Voltage-operated ELCBs were introduced in the early 20th
century, and provided a major advance in safety for mains
electrical supplies with inadequate earth impedance. v-
ELCBs have been in widespread use since then, and many are
still in operation.
Current-operated ELCBs are generally known today as RCDs
(residual current device). These also protect against earth
leakage, though the details and method of operation are
different.
When the term ELCB is used it usually means a voltage-
operated device. Similar devices that are current operated
are called Residual-current devices.
Is This Answer Correct ? | 10 Yes | 0 No |
Answer / pravesh badoni
elcb as the name suggests earth leakage circuit breaker.
while rccb is residual current circuit breaker. any current
which remains in circuit disturbs the operation of machine
and is harmful for the ckt.rccb and elcb both are the same
thing which satisfies the purpose of disconnecting the
circuit when any residual or leakage current persists in
the circuit both are rated in milli ampers ranging in
fractions of ampere (30 ma to 80 ma).
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / sachin
RCCB is better over ELCB as RCCB is not depending on earth
leakage current but it identifies imbalance between phase
and neutral.
RCCB are also coming with 30ma rating so this should not be
comparision crieteria.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / t. eswara rao
ELCB operates at a low level of 30ma. For constructional
areas, The major protection should be for workmen. More
then 30ma current is dangerous to human being and hence ELCB
is recommended for this purpose.
Is This Answer Correct ? | 7 Yes | 2 No |
while running ,synchronous generator is being turned off.what will happen to the current flow??
We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Suppose we have long 2 core DC cables running from our DCDB in control room to the load (length of around 2 to 3 km). Do we need to protect these long DC cables from earth leakages or not? If yes how?
If a fan get trip and run in reverse direction due to system flow. Now in this condition during starting how can a VFD bring this negative speed to zero and later run in forward direction?
2 Answers Aditya Birla, Siemens,
what will happen if ac motor given dc supply?
Which machine u will prefer to use at where flameble gases are comming out & why?
what is FET
star delta starter control wiring diagram?
in CNC reference how to take? what kind of input give to the servo amplifier?
WHAT IS LIGHTNING,HOW TO CALCULATE LIGHTNING DESIGN CALCULATION?
what types of load we get from the national grid? is this capacitive or inductive?
Starting Time of LT & HT Motor
WHAT IS THE DIFFERENCE BETWEEN UNDERVOLTAGE COIL, CLOSING COIL AND SHUNT TRIP COIL OF AN ACB?