What types of testing in 11Kv Ht switchgeat during testing?
Answers were Sorted based on User's Feedback
Answer / n.venkidusamy
I think that site tests.ie. Pre commissioning Tests of
following.
1. Insulation Resistance Test for breaker and protection
and other cables
2. Check for spirit level
3. Mechanical spring charge test
4. Mechanical ON/OFF test
5. Electrical spring charge test
6. Electrica ON/OFF Both Local and remote Test
7. Contact resistance Test
8. opening and Closing timings tests.
9. Protection trip Test
10. Check for operation of Closing coil at 80% and Trip
coil at 70% rated Control D.C.voltage
| Is This Answer Correct ? | 14 Yes | 0 No |
I belive you mean commisioning tests.
some of them are,
A)INSULATION TEST
b)contact resistance test
c)HV holding test
d)primary and sec injection test on the protection cct
e)transformers insulation, ratio test,vector group, insulating
oils dielectric tests.
f)cables insulation, phasing test
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / mriganka das
Transformer:
1)IR Test
2)Magnetising Current Test
3)Magnetic Core Balance Test
4)Vector Group Test
5)Ratio Test
6)Polarity Test
7)Oil Test (DGA,Dielectric Strength,Moisture content)
8)RLA test (Dirana, Thuran)
Current Transformer :
1) Ratio Test
2) IR Value Tset
3) Polarity Test
4) Knee Voltage Check
5) Winding Resistance Test
6) Back to Back Test
7) Tan Delta Test
8) High Voltage Test
Breacker Test:
1) IR Value Tset
2) Contact Resistance Test
3) Closing Tripping Timing Test
4) High Voltage Test
Isolator Test:
1) IR Value Tset
2) Contact Resistance Test
3) Closing Tripping Timing Test
4) High Voltage Test
5) Hot point Check ( in running condition)
| Is This Answer Correct ? | 7 Yes | 1 No |
Give details on how you intend to handle a challenging position you are posted to manage unexpectedly as a company staff?
AIR GAP IS TERMED AS USEFUL. WHY?
In which working principal temperature transmitter work.explain in detailed.
what is multiplying factor of a energy meter connected with a CT ratio of 600/5 and voltage at 415 volts.
up to what extwnt of voltage the celing fan works?
what is use of starter motor in DG ?
How to calculate LT XLPE CABLE for 11 kv / 433 v , 1000 kva oil type transformer system?
on whcih cycle does gas turbine works?
how can we minimize the off load losses of a distribution transformer which is required to be energized 24x7 ?? capacity of the T/F is 1250 KVA and off load losses are around 2.0 KW.. can we use capacitor bank at the secondary of such a T/F to overcome off load losses? please elaborate briefly...thanks
when we r using single phase load and we have power cable of 3.5core with .5 of neutral and neutral is suppose to the returen path of the phase how much current will flow in the neutral.reply.
Which system use dc to dc high voltage gain A. Solar system B. Battery backup
does not the circulating current in a transformer affect the flux distribution in the transformer core
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)