Why Boiler Drum level transmitter (TX) or level transmitter
rang always put -600 to 0 other -900 to 0. Mines range why
use….?
Answers were Sorted based on User's Feedback
Answer / radha
this is called wet leg system,so you are telling range -600
to 0 means your drum distance between HP & LP 600 mm and HP
and LP legs both are filled with condensate(water)
continueosly but LP leg distance higher than the HP leg,so
LP side pressure will acting 600mmWC extra, compare with HP
leg pressure,so we have to eliminate that pressure LP
pressure 600mmWC
thats why -600mmWC = 4mA
0 mmWC = 20mA
| Is This Answer Correct ? | 23 Yes | 7 No |
Answer / automatic
the negative value used for wet leg level transmitter that
means, you have the HP side filled with a reference liquid,
a initialy you should entre the pressure value of this side
in considiration that's why when we isolate the transmitter
from the vessel we never drain the HP leg
| Is This Answer Correct ? | 15 Yes | 5 No |
Answer / mavdiyaamit@gmail.com
I allways -600 to 0 range is used because maximum vacuum pressure ranhe is -760 mmHg so not use in -900 to 0
| Is This Answer Correct ? | 0 Yes | 9 No |
types of cable..? Use of every types of cable..?
Why we use 250 ohm resistor in series with HART protocol communication?
13 Answers Chemtrols, Instec, Sabic,
How does your previous experience relate to the job you are applying for ?
what is radar type level transmitters and its basic principle and how to calibrate it
how to calculate density?
In RTU Panel we are having several Analogue & Digital Inputs /Outputs. We are recently facing some problems over Analog inputs , which are not updating properly (But Digital Input are updating normally) Can any one tell me from where the problem is creating , we have checked PLC CPU card, Analog Input card & we reconfigured ,But still the issue is there. Issue : 1. Sometimes Analog values are updating & sometimes not. 2. Analog values are not updating normally , showing some wrong Values 3. Total dead (0 value) Analog values are Level & flow measurement from the field instruments. (But in field the instruments are working normally & Displaying the values normally in local display unit) This problem we are facing in our Water Plant. If any one experienced this same problem or having any ideas related to our issue PLS send your valuable Answers/Replies...
What is the difference between PLC-HMI and DCS as each function of DCS based system is possible in PLC ?
why we use 250 ohms across HART CALIBRATOR DURING CALIBRATION OF TRANSMITTER
ORP sensor working principle?
what is PID n give me brief info. about P&I&D.
suppose, after calibrating a transmitter we fixed it in a process line. At live zero condition the Tx shows 4.5 mA. what should we do to make the Tx show 4 mA? If we adjust zero, will it not affect the calibration?
I am going to attend a recruitment drive by Schneider in 2 weeks. They have a technical test in the beginning. I would like to know what are the areas i should concentrate on while preparing for the test. My major is Electronics and Instrumentation.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)