Why Boiler Drum level transmitter (TX) or level transmitter
rang always put -600 to 0 other -900 to 0. Mines range why
use….?
Answers were Sorted based on User's Feedback
Answer / radha
this is called wet leg system,so you are telling range -600
to 0 means your drum distance between HP & LP 600 mm and HP
and LP legs both are filled with condensate(water)
continueosly but LP leg distance higher than the HP leg,so
LP side pressure will acting 600mmWC extra, compare with HP
leg pressure,so we have to eliminate that pressure LP
pressure 600mmWC
thats why -600mmWC = 4mA
0 mmWC = 20mA
Is This Answer Correct ? | 23 Yes | 7 No |
Answer / automatic
the negative value used for wet leg level transmitter that
means, you have the HP side filled with a reference liquid,
a initialy you should entre the pressure value of this side
in considiration that's why when we isolate the transmitter
from the vessel we never drain the HP leg
Is This Answer Correct ? | 15 Yes | 5 No |
Answer / mavdiyaamit@gmail.com
I allways -600 to 0 range is used because maximum vacuum pressure ranhe is -760 mmHg so not use in -900 to 0
Is This Answer Correct ? | 0 Yes | 9 No |
admittance level sensor meaning?
what is function of sensor, and how is it work , explain with difination
0 Answers Bapco Bahrain Petroleum Company,
why use 4-20mA in the field of instrumentation?
what is meant by turn down ratio?
How INtools is useful for routine Instrument maintenance?
diff between neutral ,ground,phase , earthing and shielding?
Linear amplifier.
please can anyone tell me in detail, what's mean by open loop and close loop?
what is the difference between 2 wire and 3 wire RTD- application wise,cost effectivity?
what is difference between HART communication and BRAIN communication?
What is the SCAN time of a DCS/PLC? What is the typical value for scan time of DCS and PLC?
6 Answers Essar, Gasco, Siemens,
protection relay watchdog contact operation?