Answer / radha
this is called wet leg system,so you are telling range -600
to 0 means your drum distance between HP & LP 600 mm and HP
and LP legs both are filled with condensate(water)
continueosly but LP leg distance higher than the HP leg,so
LP side pressure will acting 600mmWC extra, compare with HP
leg pressure,so we have to eliminate that pressure LP
pressure 600mmWC
thats why -600mmWC = 4mA
0 mmWC = 20mA
| Is This Answer Correct ? | 23 Yes | 7 No |
Answer / automatic
the negative value used for wet leg level transmitter that
means, you have the HP side filled with a reference liquid,
a initialy you should entre the pressure value of this side
in considiration that's why when we isolate the transmitter
from the vessel we never drain the HP leg
| Is This Answer Correct ? | 15 Yes | 5 No |
Answer / mavdiyaamit@gmail.com
I allways -600 to 0 range is used because maximum vacuum pressure ranhe is -760 mmHg so not use in -900 to 0
| Is This Answer Correct ? | 0 Yes | 9 No |
HOW CAN I CONNECT ROSEMOUNT 3300 LEVEL TRANSMITTER TO Allen-Bradley SLC500
yogokowa field bus system transmitter all's we are geting IOP fault in Contiunes please help me fine how we can normal the broblems?
A differential pressure transmitter is configured to measure the height of an open tank : height 10m and dia 5m. Suppose this same transmitter is shifted to another open tank : height 10m and dia 4m. What will be the %error in measurement? how?
draw shematic diagram of c/v positioner(smart type)?
Any one can help me to identified, how can we interchange the device in FF
What is the difference between radar and ultrasonic level transmitter? Which method is best and more accurate?
We have yokogawa cs3000 one fcs and 4 his. After download to his, showing successfully at es, but not transferred to his.
What is the differerence between hysterisis and linearity.
In dcs contol valve parameters showing like this Gain=1 or 2 , ti=7 sec, td=20sec. But temp,pressure,level control valves we are using in which type parameter side using ti,td clearly tell me
what is the difference between RTU & MTU in SCADA system?
What is megering????
What is difference between profibus and modbus communication
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)