Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why the generating station rating is in KW though the
rating of generators in KVA?

Answers were Sorted based on User's Feedback



Why the generating station rating is in KW though the rating of generators in KVA?..

Answer / vittal

generating station main aim is to meet the load which can
be met completlely by the mechanical units or the source of
the prime over ,which must be mention in kw.
where as the rotationg ac machines are rated in kva
because of the losses ie the iron and copper (not on pf)
mention in kva

but even the pf is also mention on the alternator which
means the generator should be operated on that load

ex: if rating of the plant is 100 then if alternator of 0.8
pf is selected the rating of the generator must be 125

Is This Answer Correct ?    8 Yes 0 No

Why the generating station rating is in KW though the rating of generators in KVA?..

Answer / satya

though generators rating in kva ,but station rating must be
in kw . because we have to exlpress the output power interms
of true power

Is This Answer Correct ?    9 Yes 3 No

Why the generating station rating is in KW though the rating of generators in KVA?..

Answer / harish

Reason for load is not constant that time powerfactor was
change,so its call to KVA

Is This Answer Correct ?    3 Yes 2 No

Why the generating station rating is in KW though the rating of generators in KVA?..

Answer / jaggannath swami

All the loadd received by any generators is known by kilowatt i.e. kw bcose its a source of power . whoich I calculated in terms of kw The equipment rating is shown by kva & its depends upon the calculation whatever we used

Is This Answer Correct ?    0 Yes 0 No

Why the generating station rating is in KW though the rating of generators in KVA?..

Answer / m.pushparaj

in generating station power is not based on the power
factor but the generator based upon the connecting
load,that is apparent power.

Is This Answer Correct ?    0 Yes 0 No

Why the generating station rating is in KW though the rating of generators in KVA?..

Answer / electrical testing engineer

Generators are also rated in KVA. In our general terms we use terms 30KW machine but actually technical rating of any generator is in KVA.
All equipment which can supply the power are rated in KVA, because their O/P power will depend on the load type you connect with it. 45 MVA machine can give as high as 36 MW power if you improve the PF or other machines are pumping enough reactive power in the network. Thus generator Watt will vary depending on the load same as the transformers. transformers too can operate on varying degree of the MW loads depending on the load connected.
Only electrical loads such as motor, heaters are mentioned in KW.

Is This Answer Correct ?    0 Yes 0 No

Why the generating station rating is in KW though the rating of generators in KVA?..

Answer / rakesh

generater rating is in kw becoz losses in generator mainly
depends on voltage and current and not on nature of load....

Is This Answer Correct ?    3 Yes 4 No

Why the generating station rating is in KW though the rating of generators in KVA?..

Answer / gopal lal

bcoz of he load type is not fixed for any generation plant
Load to be depended in requirment of the client and
production of the plants.So dont rating KW of the any
generation plants.

Is This Answer Correct ?    1 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

how calculate gd2 of ht motors

4 Answers   Hindustan Copper Limited, Kohler India,


How to differentiate 220 Kv & 132 Kv line transmission tower if there are no specifications given on towers?

3 Answers   Karam, Power Grid,


I got shortlisted in RRB thiruvananthapuram for the post of Junior Electrical engineer, waiting List - 7. i want to know about the validity of the current list and chance to get the job please help anybody knws abt it,, thank you

1 Answers  


what is rated speed?

4 Answers   Actavis,


What is the output voltage of a DG set.

3 Answers   Fitness First,


WHY AREWE USING THE 3 1/2 CORE CABLES IN POWER TRANSMISSION

1 Answers   Phoenix Technologies,


What are the causes of electrical faults?

1 Answers  


What is Negative Potential Bias

0 Answers   TATA,


At the time of 1st charging of transformer, there were huge inrush current, so why at that diffrential relay are not operated? Why?

3 Answers   Adani,


Whatis the procedure for getting Electrical (light) licence while Iam a diploma holder in electrical Engg . I Compleated my one yr Apprentice training & worked as a junior engineer (ele) for 2 yr(contract basis).

1 Answers   TVS,


what is different the DOL Starter and Star Delta STARTER

12 Answers   Schwing Stetter,


75kw drive operated motor current fluctuation from(85-130)ampere.current setting in drive is 130amp.sometimes motor trip when current limit cross 130amps.I change the drive. still current fluctuate between 80-130amps but in this time motor not trip,current setting in drive is 130amps.where is the problem?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)