if u have single phase load (un balance) and the main power
cable is 3.5core means netural is .5 of phase and can the
three phase current make the return paht in .5 neutral.
Answer / raj
If you use all 3ph ( R,Y,B Core of Cable ) for single phase
load then only unbalanced current will flow through neutral
(1/2 Conductor ) but we must try to balance current in all
R,Y,B Phases.If you have to use only one single phase
circuit then use R+Y for Phase and B+Black for neutral (
Use twin Core to get more rating outout ).
| Is This Answer Correct ? | 0 Yes | 0 No |
In power transformer tappings are provided on A high voltage side B low voltage side C In middle of both the windings D both high and low voltage side
What are the steps for Testing of 6.6KV HT Panels?
what is the difference between star and delta connection?
if we want to increase the back up time of an UPS what should we do ? if we want to decrease the charging time of a battery/batteries attached with the UPS what should we do ?
The moisture in air will condense at
WHAT IS EXTENDED DELTA AUTOTRANSFORMER? WHERE WE USE THAT?
What is the 415V AC Soft starter? Explain with an example?
Tell me about Simence PLC 'BLOCK'.How many types and what for.
What is the working mechanism of OLTC in Power Transformers????
how to test YNyn0 vector group in transformer?
How to calculate main incomer rating of APFC Panel ? Let's say i want to find main incomer for 11kV, 1000kVAR Panel.
i want to model paper for section engg.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)