What is the starting current of a motor?
Answers were Sorted based on User's Feedback
Answer / partha podder
Starting current of a motor is high.The simplest way to
start a three-phase induction motor is to connect its
terminals to the line. In an induction motor, the magnitude
of the induced EMF in the rotor circuit is proportional to
the stator field and the slip speed (the difference between
synchronous and rotor speeds) of the motor, and the rotor
current depends on this EMF. When the motor is started, the
slip speed is equal to the synchronous speed, as the rotor
speed is zero (slip equal to 1), so the induced EMF in the
rotor is large. As a result, a very high current flows
through the rotor. This is similar to a transformer with the
secondary coil short circuited, which causes the primary
coil to draw a high current from the mains. When an
induction motor starts DOL, a very high current is drawn by
the stator, on the order of 5 to 9 times the full load
current. This high current can, in some motors, damage the
windings; in addition, because it causes heavy line voltage
drop, other appliances connected to the same line may be
affected by the voltage fluctuation. To avoid such effects,
several other strategies are employed for starting motors.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / mahesh chaudhari
Generally its 5 to 6 times than that of rated specified
current on motor name plate.
| Is This Answer Correct ? | 5 Yes | 0 No |
How to arrange a hous hold earthing system to keep minimum earth resistance( below 7ohms).
we have two generators different capacity on 15 MW and other 6MW at 11 KV , 15 MW gen. bus short level current 40KA,and 6MW short level current 25KA,, length of cable 100MTR between 6 MW from 15MW gen. for bus coupling . kindly tell any one can we use both NGR OR one NGR from any GEN. BOTH NGR has diff. rating. Tariq pakistan
Why the wave trap is put in Y phse only in switchyard?why not in other phases?
1 Answers IAG Automation, REL,
what is pressure relief valve in D.G ?state its function?
Why frequency fix in 50 Hz?
Why do we generate 3 Phase AC Supply? It is possible to generate 4 Phase and 5 Phase explain it?
what is MUSS?
TYPE'S OF BREKAR ,WHAT IS TRANSFORMAR & SAFTY. STARTER DOL & STAR DELTA STARTER.
EHV current carrying parts need to have smooth finish,then how can a 245kv GIS with emery finish can run so long?
The power factor of the fixed load is 0.8, now the p.f is varying from 0.8 to 0.5.
which type of effect of turbine and generator reverse power protection ?
How transformer winding & oil gets heat.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)