if we know Fault level say 25 KA , How to decide
busbar size for Distribution network of 1000 Amp
Breaker ?
Sample Calculation or Farmula Available or not ?
Answers were Sorted based on User's Feedback
Answer / bala
2nos.*60mm*1omm copper bar is enough for 1000amps breaker.
formula is available
| Is This Answer Correct ? | 13 Yes | 9 No |
Answer / ritesh m
When current is high then current density become constant.
You can calculate bus bar size by taking current density 1
J=I/S where j is current density, I current & s cross
section.
Then you can calculate size.
| Is This Answer Correct ? | 8 Yes | 5 No |
Answer / mehul g. c.
if you know the fault level of that area.
then you should find short circuit current.
if you find that then your busbar should be design for that
much short circuit current.
suppose your fault level is 25 ka & then your short circuit
current is 1500 amp. then your busbar should stand safe at
25 ka for 1 or 2 sec until your breaker tripped.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / subrata
125mm X 10mm aluminium busbar is enough for 1000a current (25kA)
| Is This Answer Correct ? | 3 Yes | 2 No |
What is the universal motor?
what is the formula of high voltage testing of three phase induction motor?
What is open delta Xformer? It's adavntages & Use?
What is AMP and KA in a MCCB and MCB
What are the effects of electrical faults?
why ups in kva ratings?
Total power capacity of india at present
How to find the maximum load that can supply by a particular(say 315kva) KVA rated transformer?
What is the maximum allowed kwa through 2.5mm cable. Electric company installed 2 electric meter at my premises . Two jumper wires of 2.5 mm are used to connect . 2 single phase meters with allowable load 6 and 3 kwa. These jumper wires are taken from a 3 phase electric meter. Meters are in open Sun. What max load these wires can take.
hai every bodi please let me know the test procedure for lightning arresters.
What do you mean by 4.44 in this transformer equetion E=4.44 nfqm
in 11kv generators the neutral point is connected to earth via earth coil while in the 33 / 11 kv transformer the neutral point is connected to earth via earth resistor why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)