if we know Fault level say 25 KA , How to decide
busbar size for Distribution network of 1000 Amp
Breaker ?
Sample Calculation or Farmula Available or not ?
Answers were Sorted based on User's Feedback
Answer / bala
2nos.*60mm*1omm copper bar is enough for 1000amps breaker.
formula is available
Is This Answer Correct ? | 13 Yes | 9 No |
Answer / ritesh m
When current is high then current density become constant.
You can calculate bus bar size by taking current density 1
J=I/S where j is current density, I current & s cross
section.
Then you can calculate size.
Is This Answer Correct ? | 8 Yes | 5 No |
Answer / mehul g. c.
if you know the fault level of that area.
then you should find short circuit current.
if you find that then your busbar should be design for that
much short circuit current.
suppose your fault level is 25 ka & then your short circuit
current is 1500 amp. then your busbar should stand safe at
25 ka for 1 or 2 sec until your breaker tripped.
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / subrata
125mm X 10mm aluminium busbar is enough for 1000a current (25kA)
Is This Answer Correct ? | 3 Yes | 2 No |
raleigh method
What is working Priniciple of TVSS ????
generator(Deutz 550kv)is runing for 2 hours with load of 900 amp and then it goes in shutdown with alarm fault messege of speed fault although heirtz reading fixed at 50,what does that mean
how wecalculate breaking capcity of acb mcb mccb .explain with example
Why the rating of the HT breakers are in 1250 Amp, while the load on the breaker is around 50 Amp. ?
In PFI plant one stage capacitor connection is directly connected(with out megnetic contact controll). but why?
if a motor is running at 1500rpm then how you can find its HP
What will happen if 2 phase supply is given to 3 phase motor?
wat is power factor
DG drop how much freqency at 100% load?
What type of a DC motor would you use for a lift?
in small capacitor we use uf( micro farad) and in big quantity we used kvar. i want to know that in 1 kva how much will b uf(micru farad).