if we know Fault level say 25 KA , How to decide
busbar size for Distribution network of 1000 Amp
Breaker ?
Sample Calculation or Farmula Available or not ?
Answers were Sorted based on User's Feedback
Answer / bala
2nos.*60mm*1omm copper bar is enough for 1000amps breaker.
formula is available
| Is This Answer Correct ? | 13 Yes | 9 No |
Answer / ritesh m
When current is high then current density become constant.
You can calculate bus bar size by taking current density 1
J=I/S where j is current density, I current & s cross
section.
Then you can calculate size.
| Is This Answer Correct ? | 8 Yes | 5 No |
Answer / mehul g. c.
if you know the fault level of that area.
then you should find short circuit current.
if you find that then your busbar should be design for that
much short circuit current.
suppose your fault level is 25 ka & then your short circuit
current is 1500 amp. then your busbar should stand safe at
25 ka for 1 or 2 sec until your breaker tripped.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / subrata
125mm X 10mm aluminium busbar is enough for 1000a current (25kA)
| Is This Answer Correct ? | 3 Yes | 2 No |
What is the normal earth resistance?
What is voltage in two phase?
What is difference between stable and steady?
One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?
how can we chacke adiod in a circuit
Can Dy11 and Dy1 vector group transformers be paralleled?
two generator runnig with parallel but only one NGR on And one off Why
why we use tapechanger in primary side of transformer
is it possible to use a tranformer to regulate an unstable system voltage?
how can we calculate fault current of a line in a 6 bus syatem if the faulted line is known?
can we use ordinary transformer in place of autotransformer?give reasons also
what is cathodic protaction?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)