What will be the capcity of 3 phase DG set require for 25
KVA single phase lighting load?
Answers were Sorted based on User's Feedback
Answer / mrfbdr
Approximately 3-Ph 10kva Diesel generator will be enough
considering future loads too.
| Is This Answer Correct ? | 9 Yes | 6 No |
Answer / b.dhanasekaran
dg set we normally connect 75% of it,s capacity of dg, so
in lighting load single ph is 25 kva/3=8.33kva,
so nearest 3 phase dg is 15kva,
we can use 75% so 11.25 kva lighting load @ 3 phases you
can connect.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / mel holmes
A 75kVA 3-phase generator is required to supply a 25kVA
load.
Consider a 75kVA, 400V, 3ph, 50Hz, 0.8pf DG set.
Full load current is 108A
A 25kVA 1ph load will require 108A.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / rajiv garg
25kva dg also work but this will run 100% all time.
So u have to take some margin as DG mfg suggest as given
below.
for 25kva lighting load u have to use single phase
25/.8=31.25kva dg. available dg is 33kva
so u have to go for 33kva dg.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / varma
can anyone explain more?
how can 10kva dg supplies load of 25kva(20kw)?
| Is This Answer Correct ? | 2 Yes | 6 No |
We can use 25 KVA Generator, but generator run as 100 %.
generator is over load.
pls we can use 25 KVA to 40 KVA Generator.
| Is This Answer Correct ? | 5 Yes | 10 No |
Answer / ashish
Here Your Load Is 25 KVA lighting load,& Incase Case Of
Lighting load The Load Diversity factor Factor Is Consider
as 1 so on Basis Of That We Must required 25 KVA 3Ph
generator ....but There May Be Possibiliry that All
Lighting Can Not Be ON.
| Is This Answer Correct ? | 1 Yes | 7 No |
what is the difference between energy efficient and high efficiency motors
What is reason to get a power factor nearly zero in resistive loads
why ht motor connection in star
Is it true that IPT are more accurate than CVT for Measuring purpose?
DIFFERENCE BETWEEN NORMAL TRAFO AND THRISTER TRAFO?
for measuring current and etc.,why we use value of 1.732 in three phase calculation. not in single phase.why
WHAT WILL HAPPEN IF INPUT SUPPLY OF RCBO IS CONNECTED TO OUTPUT SIDE
what is the meaning of DSL
how convert kvar to microfarade? circuit diagram of infrared transmiter and receiver? circuit diagram of Fm transmiter and receiver?
explain the Trip supervision circuit
Transformer rating=> 15/20 MVA.Why there are two raings? What should be the rating of the fuse at the secondary if the voltage level is 13.8KV/4.16KV?
I'm looking for a manual set for a Credence ASL-1000 or ASL 3000. Softcopy would be preferred but I'll take what I can get.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)