What will be the capcity of 3 phase DG set require for 25
KVA single phase lighting load?
Answers were Sorted based on User's Feedback
Answer / mrfbdr
Approximately 3-Ph 10kva Diesel generator will be enough
considering future loads too.
| Is This Answer Correct ? | 9 Yes | 6 No |
Answer / b.dhanasekaran
dg set we normally connect 75% of it,s capacity of dg, so
in lighting load single ph is 25 kva/3=8.33kva,
so nearest 3 phase dg is 15kva,
we can use 75% so 11.25 kva lighting load @ 3 phases you
can connect.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / mel holmes
A 75kVA 3-phase generator is required to supply a 25kVA
load.
Consider a 75kVA, 400V, 3ph, 50Hz, 0.8pf DG set.
Full load current is 108A
A 25kVA 1ph load will require 108A.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / rajiv garg
25kva dg also work but this will run 100% all time.
So u have to take some margin as DG mfg suggest as given
below.
for 25kva lighting load u have to use single phase
25/.8=31.25kva dg. available dg is 33kva
so u have to go for 33kva dg.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / varma
can anyone explain more?
how can 10kva dg supplies load of 25kva(20kw)?
| Is This Answer Correct ? | 2 Yes | 6 No |
We can use 25 KVA Generator, but generator run as 100 %.
generator is over load.
pls we can use 25 KVA to 40 KVA Generator.
| Is This Answer Correct ? | 5 Yes | 10 No |
Answer / ashish
Here Your Load Is 25 KVA lighting load,& Incase Case Of
Lighting load The Load Diversity factor Factor Is Consider
as 1 so on Basis Of That We Must required 25 KVA 3Ph
generator ....but There May Be Possibiliry that All
Lighting Can Not Be ON.
| Is This Answer Correct ? | 1 Yes | 7 No |
i have total 8 dg sets for synchronizing and 2 buscoupler,1 sectoin dg no 1,2,3,and 2 sectoin dg no 4,5,6,and last section dg no 7,8 ....if buscupler no 1 and 2 is off mode ..than dg no 1,2,3,will synchroniz of another dg sets?
what does a k rating in a transformer means?
How to calculate Busbar Thickness for Different type of HT/LT panels
Clearly Define Active,Reactive,Apparant power.Which applications used which power above metioned power?
Which one is easy to control AC or DC Machine?
What is power distribution criteria for converting single phase unbalanced residential load to 3 phase star connected balance system. Does total KW converted to 3 Phase. Means Divided by root 3.
why Square root 3 used for three phase?
what is encoder & its use?
What are the specifications for conducting earth leakage test as per IEC standard?
how to calculate the current carring capacity of the conductor
what are doing the duall connetion in tree phase 10hp or etc motor with circuit diagram
hi, is there a difference in choosing bus bar for DC or AC ,,if there can anyone help me about. thanks
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)